Gravity system
Ryan Metivier
Member Posts: 1
I need to replace a 104 year old gravity boiler in a 2 story house with a demand of 72k demand acording to the radiator sizes. The system is split with 2 3" supplies and 2 3" returns for close piping. I can not find any boilers with that size and amount of tappings. The Utica boiler has 2 2" supply tappings and one return. Can I use this configuration and tee the return and still have enough flow? Circulators are unfortunately not an option.
Ryan
circs not an option?, ever considered this? , it may have the tapping sizes you`re looking for.
Always try not to use a standing count though, HL calc is the best method.
Dave0 -
boiler sizing
Use total radiation (radiator size/count) for steam, but use structure heat loss for hot water systems.
Why isn't a circulator an option?0 -
My overhead gravity system was converted
Not a pro here, but my old overhead gravity system uses a 6 inch(I think) riser and return, but were reduced to 1.5" to connect to the boiler and circulator sometime around 1991.
And this reduction was original to the system.
Since I assume you would be converting to a closed circulated system, why can't you use circulators since convection isn't going to be the vehicle anymore?
More than anything else, I am just curious what the barrier is for this application.
AlThere was an error rendering this rich post.
Al & scrook,
maybe he`s Amish?, just a thought, but could be?
Dave0 -
Gravity
The Weil McLain EG series is a good choice here.
It is the ONLY WM boiler I will install.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"There was an error rendering this rich post.
- 87K THE MAIN WALL
- 116 Chimneys & Flues
- 107 Geothermal
- 983 Plumbing
- 389 Solar
