boiler piping correct way
Options
burnerman_2
Member Posts: 297
ok we are having an argument on this so let me have some feed back on a hot water boiler that maintains temp and u install a flo-check valve can itb before the air scoop with the exspansion tank located there also i thought it had to be air scoop then the flo-check my buddy says the expansion does not matter unless there is zone valves so which is it or either way ok ????
0
Comments
-
Order, Order
The flow check wants to go at the outlet of the circulator.
The expansion tank connection wants to be at the suction (inlet) side of the circulator.
The air scoop is also best installed at the inlet of the circulator, the fact that most have provisions to install the expansion tank there is no small coincidence and certainly is convenient."If you do not know the answer, say, "I do not know the answer", and you will be correct!"
-Ernie White, my Dad0
This discussion has been closed.
Categories
- All Categories
- 87.4K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 167 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements