combustion test question

Options
Thank you that was the info I was looking for.

Comments

  • curiousity kills
    curiousity kills Member Posts: 118
    combustion test question

    When checking flue with Testo or like on a fha system once o2 stabilizes, if I disconnect blower and o2 drops and then goes back when blower is on,1.would this indicate a breech in a hxchanger 2. what % change is acceptable.Thanks for any info.
  • Robert O'Connor_11
    Robert O'Connor_11 Member Posts: 42
    Generally

    yes. No change would be acceptable. However if the blower is depressurizing the room you might see a change.

    All

    The best

    Robert
  • Steve_35
    Steve_35 Member Posts: 545
    Does the breech pressure change as the blower comes on?

    If so, that may indicate problems with the duct work. Disconnected returns, especially if the unit is in a confined or semi-confined space, can cause pretty dramatic changes in the vent pressure.

    We had a customer a few years back who installed their own furnace and was convinced they had a bad heat exchanger. Furnace in a fairly small area with about a 6" gap between the side of the furnace and the RA grille opening into the rest of the house. Blower came on and the breech went from about -0.04"wc to +0.10"wc.
  • Mark Hunt
    Mark Hunt Member Posts: 4,908
    Some \"intersting\" returns

    Here are a few pics of some returns we have seen.

    Some done by the HO and some by "pros".

    Enjoy!

    Mark H

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Mark Hunt
    Mark Hunt Member Posts: 4,908
    O2 rieses


    when blower starts, then you are pushing air into the flue gas.

    O2 drops when fan starts, you're depressurizing the room.

    What were your other readings?

    Mark H

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • curiousity kills
    curiousity kills Member Posts: 118
    Reply

    Thanks for your replies.Mark how can this depressurize on a sealed combustion 90% where are is drawn from outside?First I would jumper door switch run system until all numbers stabalize then pull door and remove blower common wire the o2 dropped 3%. 8 down to 5. Then when I plugged the common back in it rose to 8 again.Thanks for any replies
  • S Ebels
    S Ebels Member Posts: 2,322
    Pondering out loud, and a thousand pardons Hunt.........

    Don't want to horn in on your conversation here but............

    Is it truly a sealed combustion unit? Some manufacturers claim sealed combustion but due to missing gaskets, door seals or ill fitting sheet metal covers.........they kind of miss the target. If it isn't sealed then you have the blower acting as an outside influeance on the combustion process. (influeance........pun intended)

    What are the other gases doing while the O2 is changing? CO and CO2 specifically. Is the CO solid or does it change. When your O2 goes up the CO2 should go down and vis-versa. Is this happening?

    Were both tests with the blower door on or did you leave it off in the second scenario (blower not running)

    How old is the unit and what brand?

    Typically, when I see a change of that magnitude, I start looking around inside. Especially so if the CO is flopping around.
  • curiousity kills
    curiousity kills Member Posts: 118
    reply

    In both tests blower door was closed.Co remaind the same 5ppm.
  • S Ebels
    S Ebels Member Posts: 2,322
    And

    What about the CO2?
  • curiousity kills
    curiousity kills Member Posts: 118
    reply

    Im not sure but wont co2 change on the testo whenever oxygen changes
  • Rudy
    Rudy Member Posts: 482
    Yes

    All manufacturer's analyzers calculate the CO2 reading based the O2 reading - there are no CO2 sensors in the instruments, only O2 sensors.
  • curiousity kills
    curiousity kills Member Posts: 118
    reply

    I appreciate the responses but my original question has yet to be answered
  • S Ebels
    S Ebels Member Posts: 2,322
    I would be highly suspicious

    Highly suspicious indeed of the HX in that furnace. Something is amiss somewhere that is causing the variance in your readings, blower on vs blower off. It shouldn't be doing that. The thing is, depending on the location of the crack or hole the combustion chamber can be pressuruzed or de-pressurized. It depends on where exactly the breech on the HX is located. Some areas will see a positive pressure, for example, a loaction where the metal is curving outward into the air flow. The reverse is true of an area that is "sheltered" from direct airflow. This would be an area "hidden" from the airflow such as on the downstream side of a curved portion in the HX.

    You da man on the job here but if it were me, I'd be peeling sheetmetal back and searching for the problem. That much variation in your O2 is not a good thing regardless of what is causing it. That's the bottom line IMHO.
  • toearly_2
    toearly_2 Member Posts: 78


    What brand of furnace ??

    Does it have a clam shell HX ?

    David

    > Thank you that was the info I was looking for.


  • curiousity kills
    curiousity kills Member Posts: 118
    reply

    Concord 90% approx 6years old. Not sure if the primary is clamshell.
  • toearly_2
    toearly_2 Member Posts: 78


    The age is about right.

    On Serpentine HX from ICP I am finding the rings that hold the two halves together are falling out. These rings are located in the center of the sections. When they fail they allow air to infiltrate into the HX rather then out. If enough rings fail heat will roll out the front of the burners. The presssure switch will not shut off the furnace in this type of failure.

    I do not know if you have an ICP HX in your furnace. But it is worth looking at.

    David

    > Concord 90% approx 6years old. Not sure if the

    > primary is clamshell.


  • Steamhead (in transit)
    Steamhead (in transit) Member Posts: 6,688
    Another argument in favor of hydronics

    this would never happen with hot-water or steam heat.

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • toearly_2
    toearly_2 Member Posts: 78


    No Doubt about it.
    When I first moved from NJ to Upstate NY I was like a fish out of water. 95% of all heating in this area was scorched air. To see someone heat their home with nothing but wood was an even bigger shock.

    David


    > this would never happen with hot-water or steam

    > heat.

    >

    > _A
  • curiousity kills
    curiousity kills Member Posts: 118
    reply

    Thanks for the info. I have seen the same problem with Goodman.
  • jim lockard
    jim lockard Member Posts: 1,059
    David

    If what you say about the rings falling apart between HX's I should be able to turn on the indoor fan, drill a 1/4 hole in the pvc vent pipe, insert my Mag gage probe and find pressure?. I may have to block the flue and fresh air pipe in order to have a reading if its a small leak but I should find pressure. Then by turning the fan off I should lose pressure correct. Thanks J.Lockard
  • toearly_2
    toearly_2 Member Posts: 78


    No. You should not see any change
    The primary HX is under a constant negative pressure from the inducer. The outlet side of the inducer should also remain a constant number. The inducers are made to move X amount of air it does not matter where it comes from. With the serpentine HX you are going to have an in shot burner. When the rings fail we are only talking a few thousands on an inch for air leakage. This places an air curtain in the HX that will change the combustion numbers and then as more fail hinder proper venting in the HX. I have replaced about a dozen of these HX so far and have not found any soot in the HX and have only had one that shut off on the limit switch located at the burner assy . We caught all but one during normal servicing.

    If you watch the burner from start up and wait for the blower to come on. You will see the flame spread out in the HX if a ring has failed

    A combustion analyzer will also tell you something has changed

    We drill a hole in the plenum and use our camera to find the rings sitting on top of the secondary HX.

    David

    > If what you say about the rings falling apart

    > between HX's I should be able to turn on the

    > indoor fan, drill a 1/4 hole in the pvc vent

    > pipe, insert my Mag gage probe and find

    > pressure?. I may have to block the flue and fresh

    > air pipe in order to have a reading if its a

    > small leak but I should find pressure. Then by

    > turning the fan off I should lose pressure

    > correct. Thanks J.Lockard



  • Jim Bergmann_2
    Jim Bergmann_2 Member Posts: 79
    O2 testing heat exchangers

    If a furnace passes the ventilation air test as outlined in the International Fuel and Gas Code (Appendix D) the O2 test will produce valid results and depressurization due to duct leakage or other venting problems will not effect the results.
    The O2 test has several advantages over the trace gas test including testing during normal operation under normal temperatures. Leaks below the burner will be evident. Multiple tests can be performed at once including combustion air testing, heat exchanger testing, CO testing, and efficiency testing. A combustion analyzer can be used to determine unacceptable leakage, atmospheric draft appliances and draft-induced appliances using O2 as the trace gas. The O2 will be below 21% and stable during normal operation. When performing this test, it should be noted that as of this writing, there has been no formal field study to document the correlation of minimum leakage rates and O2 changes. However, during lab testing, we were able to determine leakage through a single 1/8” test hole drilled in several locations in the heat exchanger. After each test the hole was plugged with a screw and an additional location was tested. Multiples of holes were also tested to simulate pin holing in a heat exchanger. Locations were specifically selected that avoided air blowing directly in the heat exchanger, and rather depend upon system static pressure to force additional air from the supply side into the heat exchanger. If the O2 changes when the blower starts, there is leakage into the heat exchanger, and further investigation is warranted. Closing main dampers will increase supply side static and further amplify the leakage rate. If cracks or holes cannot be found, the customer should still sign off in writing that they have been notified there is a potential problem with the operation of their furnace.

    PERFORMING the O2 TEST
    A flue gas combustion analyzer can be used effectively for finding leaking cracks or holes in a furnace heat exchanger. Not all cracks or holes will leak. Smaller cracks and holes found only by a thorough visual inspection may not be leaking during the time of testing. They still pose an potential danger to your customer, as cracks will continue to open over time due to the tremendous forces on the metal at the ends of the crack.

    On all furnaces the static pressure achieved by the system blower can overcome any positive pressure in an atmospheric draft appliance. On draft-induced appliances, the pressure within the heat exchanger is always negative, causing them to leak in rather than out. Any leakage in a heat exchanger in or out poses a danger to your customer. Leaks out can allow flue gasses that may contain CO into the living space, and pressurization of a draft induces appliance heat exchanger can result in a rollout and possible fire. With all combustion, the readings on the analyzer should be stable after several minutes. When the stack temperature stabilizes, all other gas readings on the analyzer should also remain stable. Readings that change during operation after stabilization has taken place are indicative of a combustion air, venting, or mechanical problem such as a cracked heat exchanger.

    Important notes:

    1. Oil furnaces and older gas appliances can have cleanouts leaking that will test positive for leakage. This is not a heat exchanger failure. Inspection gaskets should be replaced and properly sealed following the manufacturer’s recommendations. If the manufacturer’s recommendations are not available, an industry-approved method should be used to seal the cleanout.

    2. No inspection method is “fool proof.” The three-part method should always be performed to maximize the safety of the appliance.

    PROCEDURE:

    1. Follow the manufacturer’s instructions to properly zero the combustion analyzer.

    2. Insert the combustion analyzer in the appropriate test position in the furnace.
    a. For atmospheric draft appliances this would be directly in the heat exchanger cell.
    b. For 80+/90+ furnaces this would be in the stack.

    3. Start the furnace and observe the oxygen reading for stability. (1-3 minutes)

    4. When the blower starts, watch for a change in the O2 reading. If the blower starts prior to stabilization of the O2 reading, a piece of cardboard can be inserted and removed during operation to observe if any changes in the combustion readings take place.

    Corrective action:
    Attempt to visually find the crack or hole.
    A. If you can find the defect, show it to the customer.
    B. On the service invoice, write that your testing indicates a leak in the heat exchanger. (Do this even if you cannot find the leak.)
    C. Inform the customer, in writing, that the heat exchanger has a defect and poses a potential danger. (Do this even if you cannot find the leak.)

    Hope this helps
    Jim Bergmann
    HVAC/R technical Specilist
  • Jim Bergmann_2
    Jim Bergmann_2 Member Posts: 79
    O2 testing heat exchangers

    If a furnace passes the ventilation air test as outlined in the International Fuel and Gas Code (Appendix D) the O2 test will produce valid results and depressurization due to duct leakage or other venting problems will not effect the results. The O2 test has several advantages over the trace gas test including testing during normal operation under normal temperatures. Leaks below the burner will be evident. Multiple tests can be performed at once including combustion air testing, heat exchanger testing, CO testing, and efficiency testing. A combustion analyzer can be used to determine unacceptable leakage, atmospheric draft appliances and draft-induced appliances using O2 as the trace gas. The O2 will be below 21% and stable during normal operation. When performing this test, it should be noted that as of this writing, there has been no formal field study to document the correlation of minimum leakage rates and O2 changes. However, during lab testing, we were able to determine leakage through a single 1/8” test hole drilled in several locations in the heat exchanger. After each test the hole was plugged with a screw and an additional location was tested. Multiples of holes were also tested to simulate pin holing in a heat exchanger. Locations were specifically selected that avoided air blowing directly in the heat exchanger, and rather depend upon system static pressure to force additional air from the supply side into the heat exchanger. If the O2 changes when the blower starts, there is leakage into the heat exchanger, and further investigation is warranted. Closing main dampers will increase supply side static and further amplify the leakage rate. If cracks or holes cannot be found, the customer should still sign off in writing that they have been notified there is a potential problem with the operation of their furnace.

    PERFORMING the O2 TEST A flue gas combustion analyzer can be used effectively for finding leaking cracks or holes in a furnace heat exchanger. Not all cracks or holes will leak. Smaller cracks and holes found only by a thorough visual inspection may not be leaking during the time of testing. They still pose an potential danger to your customer, as cracks will continue to open over time due to the tremendous forces on the metal at the ends of the crack.

    On all furnaces the static pressure achieved by the system blower can overcome any positive pressure in an atmospheric draft appliance. On draft-induced appliances, the pressure within the heat exchanger is always negative, causing them to leak in rather than out. Any leakage in a heat exchanger in or out poses a danger to your customer. Leaks out can allow flue gasses that may contain CO into the living space, and pressurization of a draft induces appliance heat exchanger can result in a rollout and possible fire. With all combustion, the readings on the analyzer should be stable after several minutes. When the stack temperature stabilizes, all other gas readings on the analyzer should also remain stable. Readings that change during operation after stabilization has taken place are indicative of a combustion air, venting, or mechanical problem such as a cracked heat exchanger.

    Important notes:

    1. Oil furnaces and older gas appliances can have cleanouts leaking that will test positive for leakage. This is not a heat exchanger failure. Inspection gaskets should be replaced and properly sealed following the manufacturer’s recommendations. If the manufacturer’s recommendations are not available, an industry-approved method should be used to seal the cleanout.

    2. No inspection method is “fool proof.” The three-part method should always be performed to maximize the safety of the appliance.

    PROCEDURE:

    1. Follow the manufacturer’s instructions to properly zero the combustion analyzer.

    2. Insert the combustion analyzer in the appropriate test position in the furnace. a. For atmospheric draft appliances this would be directly in the heat exchanger cell. b. For 80+/90+ furnaces this would be in the stack.

    3. Start the furnace and observe the oxygen reading for stability. (1-3 minutes)

    4. When the blower starts, watch for a change in the O2 reading. If the blower starts prior to stabilization of the O2 reading, a piece of cardboard can be inserted and removed during operation to observe if any changes in the combustion readings take place. Corrective action: Attempt to visually find the crack or hole. A. If you can find the defect, show it to the customer. B. On the service invoice, write that your testing indicates a leak in the heat exchanger. (Do this even if you cannot find the leak.) C. Inform the customer, in writing, that the heat exchanger has a defect and poses a potential danger. (Do this even if you cannot find the leak.)

    Hope this helps Jim Bergmann HVAC/R technical Specilist





  • curiousity kills
    curiousity kills Member Posts: 118
    Reply

    Thank you very much for this explaination.I made a device to make this test easier.I took a lampcord switch you can buy at hd and two extra long jumperleads.I cut one end of the lead off each and wired it to the swich.Then drill a small hole in the blower door and wire the switch in series with the blower nuetral.This way the blower can be turned on and off while the system is operating with the door on.
  • toearly_2
    toearly_2 Member Posts: 78


    After these post.. I ran into a bad HX.
    It was not too hard to find this one
    Here are some pictures
    The HX was replaced the same day.

    2nd Picture ring missing

    3rd Picture ring in place

    David