What size bladder tank to replace compression tank?
Options
Brad White_33
Member Posts: 16
taking into account system volume, initial PSIA, final PSIA and your tank volume selection has some "fat" in it to cover any unforseen variables, then go with it. Personally I prefer to specify multiple tanks manifolded together should one fail. But that is just a risk assessment.
Double check your calculations and proceed with confidence in them.
Double check your calculations and proceed with confidence in them.
0
Comments
-
What size bladder expansion tank to replace compression tank
A customer of mine has a 120 gallon horizontal compression type expansion tank in their hydronic system. They want to replace it with bladder tank(s) (vertical area is a problem). My supplier is recommending two 57 gallon total volume, 27 gallon acceptance expansion tanks.
In doing my calculations, I came up with one 80 gallon total volume tank needed to convert. Naturally, one 80 gallon tank will cost less than two 57 gallon tanks (either way, ASME required).
So I ask all of you, and I know that you do not have all the data needed, should I trust my calculations, or is my suppliers recomendations more on the mark. Thanks for your help.0 -
Expansion tank conversion spreadsheet
Try this spread sheet out. This will help you with sizing.
Joe Mattiello
Technical Support Technician
Tel. 401-942-8000 X 484
Fax. 401-942-2360
1160 Cranston St
Cranston, RI 02920
joemat@taco-hvac.com0 -
Thanks guys. You were a big help.0
This discussion has been closed.
Categories
- All Categories
- 87.4K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 167 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements