Check valve for main vent?
Steve Garson_2
Member Posts: 712
Problem: Radiator "whoosh" sounds from air vent at end of steam cycle. Possible cause: Gorton main vents not opening as fast as the radiator vents, forcing vacuum to be filled from radiator making sounds that are annoying.
Someone on this site suggested installing a check valve in line with the main vent to allow air in if there is vacuum.
Can anyone provide their opinion and advice. Exactly what should I be asking for at the supply house. Are there concerns with this approach? I use three Gorton #1s on each of two mains with Gorton radiator vents. One-pipe steam with new boiler.
Steve from Denver, CO
how about
intermixing a hoffman 75 amongst the gortons..
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"gwgillplumbingandheating.com
Do you think a Hoffman 4A would do the job? I don't need to vent air out real fast, just need to let it in.Steve from Denver, CO0 -
hmmm, i don't know if
it would let it back in any faster than it lets it out...which isn't fast..
I posted a few weeks ago about putting vacuum breakers in line with my Gorton #2's.
I went ahead an installed 2 watts vacuum breakers on each end of the mains just after the last #2. I think they are working very well, the air comes in and cools the manifold I made for the Gortons (4 each end) and they open more quickly, therefore opening them up to also vent. My radiators are holding heat alot longer now.
Phillip0 -
Could I simply connect the present Gorton vent to a Tee and then attach the vacuum breaker with a nipple and elbow?
This solution makes me wonder why I haven't seen anyone with a problem similar to mine?Steve from Denver, CO0 -
i like Phillips idea..
it should solve your issue.
Phillip:
Why would the radiators hold more heat with the vacuum released?Steve from Denver, CO0 -
Phillip: Can you please post a picture of where exactly you installed the vacuum breakers? I would like to install one on my vent manifold.
Thanks
Mark Sch0 -
My Gortons were staying shut quite awhile after the boiler shut off, I am guessing due to ambeint temps near the boiler.
After shut down, the system cooled and went into a vacuum, the radiator vents opened well before the main vents did, the air was sucked into the system through the radiators cooling them down in no time.
Now the vacuum is relieved very quickly, whereas before it seemed to take a few minutes to relieve the vacuum.
Phillip0