New water heater problem!
adambuild
adambuild Member Posts: 422
Last week installed an AO Smith Model # XCV 50 100, 50-gallon water heater to replace same in a residential app and they run out of hot water after about 20 minutesd of "regular" usage!? We don't sweat near the dip tube. Any other thoughts? When I was there last week, the water was 125* at the laundry sink next to it. It's happening at all fixtures. I initially thought cold was migrating to hot side but doesn't seem to be. Any ideas? First time it's happened in all the years!
Thanks in advance, Adam
  • ed wallace
    ed wallace Member Posts: 1,612
    running out of hot water
    I would check the dip tube
  • Got circ return???
    If you have one without an operational check valve, it too can create a situation that mimics running out of hot water.
    ME
  • heating tech
    heating tech Member Posts: 2
    you could have a defective dip tube, possibly a bad unitrol did you let the tank fully satisfy and then turn on the hot water, if they dont get enough you have a cracked dip tube which will not give you enough hot water. if its happening in more then 1 area its a tank problem.
  • Larry Weingarten
    Larry Weingarten Member Posts: 4,011
    Agree...
    ... with the others. Dip tube, cross connection, or recirc line. The dip tube could have been put in the wrong side, or simply not installed. A cross connection shouldn't happen at the same time, but it could be something as simple as a shut off valve on the shower, downstream of the hot and cold valves. If there is not a working check valve in a recirc line, you will get backflow. I prefer spring check valves over swing checks in my hard water area.
    Be curious to know what you find.
    Yours, Larry
  • martin
    martin Member Posts: 144
    Low hot water
    I had something similiar happen to me several years ago. Cold water was leaking thru a moen single handle shower valve and diluting the hot.The valve was closed and didn't leak but would bleed thru. Shut the input valve to the heater and turn on a hot spigot at the lav if you have any water other than gravity that could be the problem.