Sizing Circulators
Options
Brad White_96
Member Posts: 10
that the right pump should start at the selection point, but I was asking if Taco was going to get into the variable speed business.
0
Comments
-
I assume circs sized to emitters, pipe diameter and length
of each zone. 1950s Long Island 2100 sq ft split level, two zone. (Main zone is the full house, monoflo with 1" manifold and 3/4" branches to convectors, 39mbhloss/75mbh gain; 2nd zone is rear porch only baseboard 8mbh loss/25K gain.)
One contractor has spec'ed 3 B&G NRF-22s (third one for the indirect ST-200) for Buderus G115/21. But given the disparity in the zones, wouldn't a variable speed Grundfos do better? Seems like it might need to be more specifically tailored. Contractor has the heat loss info but probably not length of run. Not sure yet if this is being done primary secondary, but are my concerns valid whether done primary/secondary or not?
I have read some of the great wall posts on sizing circulators and the consensus seems to be to do the measuring and calculating to size the circs as much as possible so you don't have to get one too big and then throttle it to make it match. This seems to be a very important part of ensuring proper and efficient delivery of heat.
Thanks,
David0 -
I am not super-familiar with
the B&G line, but do have access to the NRF-22 curve. It runs from 15 feet at no flow ("dead-head" flow) out to 22 GPM with no resistance. Mid-point is roughly 10 GPM at 8 feet of head.
For your "Baby Zone" (Jeesh why bother, just open the door!
, Might the NRF-9F/LW low wattage circulator be a much better choice? Even if you use a full 1.0 GPM (oooh!) you can deliver that against 7 feet of head. Assuming a 20 degree delta-T this is reasonable.
By comparison, a Grundfos UPS 15-42 (if they still make it?) is good for 1.0 GPM at about 11.0 feet of head even on speed 1. This may be more than you need and draws 45 Watts. The B&G draws 40, not much difference though. Your call, but only when you know the resistance.
Sight unseen and with average conditions, this does not seem out of line especially if secondary pumping is going on here.
Your prime heating zone at maybe 4.0 GPM could be met by the NRF-22 against 12 feet of head. That seems like a lot but again I have no particulars of lengths and fittings. My own house pumps 7.5 GMP against 7.5 feet more or less, but this is secondary to my boiler circulator. My distribution splits from 1.25" copper to 1" most of the way and is piped reverse-return. Round trip is about 110 LF plus fittings as a point of reference only.
I would use the smallest circulator that does the job, David, we agree. The Grundfos line is excellent but regardless of the adjustability, the selection still has to come close. I think of the 3-speed feature as being like getting three different pump models firstly, and adjustment to load secondarily.
Save the big flow for the indirect and bathe that sucker in hot water. But heating is forgiving of flow variation as you recall. If it drops by 50 percent, you will likely get 90 percent of your capacity. We all need slack in life but I hope you get more than just good flow.
Brad0 -
Taco, 007
The B&G operating characteristics are equivalent to the Taco 007 replaceable cartridge circulator. The 3 speed grundfos circulator will work, but why spend the money on a pump with multiple flow capacity when you can simply use a less expensive pump that will deliver the flow rate required to satisfy the load.Joe Mattiello
N. E. Regional Manger, Commercial Products
Taco Comfort Solutions0 -
Thanks Brad--that's a shot of fresh air
I gather we'll have to measure the length of main supply run and then lengths of 3/4" supply and returns to and from rads, and elbows and tees. Some of this might be hard to see. I guess from the monotee off the main below the 3/4" will have at least one elbow going into the convector and one out. (Though sometimes due to conditions I've seen multi-elbow combinations near the element.)
So then the head and gpm can be calculated knowing the length of run plus branches, elbows, tees, pipe diameters and heat loss. I think this measuring (estimating) shouldn't take more than 45 minutes or so.
I have been reading Dan's pumping away--but in small doses since it makes my brain hurt. Interesting you say that a drop of 50% of flow will only lose 10% capacity. But overly fast flow as I understand it--especially through baseboard--can prevent emitter from discharging the btus.
thanks,
David0 -
sometimes circs not tailored because it's more convenient
for maintenance company to keep only one or two kinds stocked in their trucks. You could have a great system installed by a company that doesn't do maintenance after the first year and then have to look long and hard to find the next company.
Same reason I am often told, "you don't need to have ball valves on either side of circ, just house side of circ and at return since it's a small system and you'll only have to drain the boiler to replace a circ. How long does that take?" I can understand the thinking; I wish things were otherwise.
David0 -
When I run into one of these
I generally look to see if the main house zone can be split. Sometimes it can be- this is great if you can put bedrooms on one zone, main living areas on another. Having the capability to run lower temperatures in areas that are not occupied will save fuel.
Monoflo systems can be tricky since the flow splits so many times. The special tees that make the system work, add a noticeable amount of resistance ("head") that the circ must deal with. The more Monoflo tees, the more resistance.
Try this: Get an infrared thermometer. Start up your system with all radiation turned on. When the return line gets warm, compare the supply line temp leaving the boiler with the return temp. You're looking for a difference of 20 degrees or so, if this is what you get the circ size is OK. If the difference is noticeably less, the circ is too big (most are). If there is too great a difference, the circ is too small.
Note that many infrared thermometers need a black surface from which to take a reading. If you have copper pipes, wrap some black electrical tape around them before taking readings.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
With all due respect, Joe
(and I do love and use Taco products), the cost difference between a 007 and a 15-42 is minor; sometimes the Grundfos is less. I consider them equal. The ability to take a pump down to 45 Watts (instant trim) is appealing. Is Taco going to offer a similar feature across their line?
Brad0 -
Valves are short money
When I want to take a shower, I go to the tub. Valves rule.0 -
thanks Steamhead--for your chart too.
Unfortunately in this case moms housewe wont be doing any splitting zones. Id guess your test would have to be done in winter, yes? to test that delta T. (delta T should always be about the same regardless of outside conditions or supply temps I assume.) theres a TACO and a grundfos currently on each zone but I dont know which on which.--have to check. From what I know Ive never heard of any heating problem or some areas colder or warmer. We hope to be installing a new boiler within a month.
Main zone (four levels) has only 12 rads including two in basement. Thats 24 monotees.
Ill see about an infra red thermometer; I do have a digital thermometer with a metal point sensor if that would suffice.
Based on your circ sizing chart, main zone's 75mbh emitters on a 'modern' system would translate to about 7.8gpm. Smaller zone would translate to 2.75gpm. So I guess one would still have to measure to calculate the head. Hard to think both zones should have same pump.
Thanks,
David0 -
I-R Thermometers
are the best invention since Data Loggers... IMHO. Plus with the laser feature you can endlessly harrass the cats.
As Steamhead says, a spot of black (paint or tape) will yield the results.
Absent an I-R thermometer, a good multi-meter might have a thermistor feature (very accurate) and can measure surface temperatures precisely.
Your measurements at the surface will be off by a degree or so from what is in the pipe, but it is the Delta you seek. All other things being equal, surface measurement is just fine. Besides with a MonoFlow system, your temperature will decay along the lenght. Each runout set to emitters should read about 20 degrees differential and the S-R differential at the boilers likewise shouls also.
Many systems work perfectly fine without any fancy balancing because flow to output can be so forgiving. But how well they do is good to know, to have a base-line. Key to the exercise is to cut down your parasitic transport losses (circulator amperage) to their minimum.0 -
My primary objective was to compare the Taco to the B&G. Secondly, compare the Taco, to the 3 speed pump monetarily, but also point out the need to simply size the pump specific to the system load, as opposed to buying a pump because of what it can do.Joe Mattiello
N. E. Regional Manger, Commercial Products
Taco Comfort Solutions0
This discussion has been closed.
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 167 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements