BTU's from PEX with extruded aluminium plates
Brad White_9
Member Posts: 2,440
And at what water temperature? Are the plates extruded or sheets? Output can be anything between 1 and 30 unless you nail down some other variables.
How many BTU's can one expect out of 3/8 pex snapped into aluminium plates...plates are on 8" centers....0 -
room temperature also
as the delta t between the floor surface and the space temperature drives the output.
Radiant Engineering has some excellent tables and graphs to show outputs a temperatures and with various floor coverings. www.radiantengineering.com
hot rod
Thermofin Output
Output based on the R-Value of the finished floor and fluid temperature with a 65°F MRT. The gray horizontal line is generally the maximum comfortable output for these conditions.
Hope this helps.0 -
That is a very nice webb site,...
But get the latest design guide from Wirsbro / Uphonor or whatever their name is...it's a simple question with a complicated answer. Some jobs we just kept adding tubing untill the customer was happy and why does each joist bay only have one run of tubing in it? That may be a problem!0
- 167 Indoor-Air Quality