Hartford loop in a boiler feed system/vacuum return
Jim Farrell_2
Member Posts: 1
We are not not certain that using a hartford loop in a vacuum return with a heat balancer and a duplex boiler feed system will provide any benefit.
Can anyone comment?
Thanks
Jim
Can anyone comment?
Thanks
Jim
If the pump is near the boiler
there's no benefit at all.Retired and loving it.0 -
Before eliminating
the Hartford Loop, you might want to check the local code. Our city requires a Hartford Loop on all low pressure steam boilers. Matters not whether return is pumped or gravity.
Ron
Where are you? Which code are you citing?
Robert O'Connor/NJ0 -
Washington, D. C.
DCMR 13B
Ron
DCMR 13B, I'm assuming this means District of Columbia Municipal Regulations section 13B. It would appear to me that this is the Administrative Code for your area and its adoption of DCMR Title 12/ Construction Code Supplements.
I briefly "googled" the DCMR, and it would appear the Administrative Code adoption(s) (with exceptions) govern the use of the International Mechanical Code. The 2003 IMC Section 1004 BOILERS/section; 1004.2 Installation. This section states that the installation shall conform to the manufacturer's installation instructions.
Do you have more detailed information?
Many medium to large boiler installations require feed units or condensate pumps that usually negate this piping arrangement and use. Although it never hurts to install one, I agree with our host in stating there is no benefit at all.
Unfortunately,
D. C. picks & chooses which parts of which codes they want to enforce. The H/ L is one of the "thou shalts." Another is the requirement for brass pipe, w/ crosses & plugs, for feed water & control piping on steam boilers.
The plumbing inspectors are OK on residential equipment. No so when the D. C. Boiler Inspection Department gets involved w/ inputs above 525 MBH. Found out the hard way, it is seldom worth the trouble to disagree. Since the subject started w/ a vacuum/feed water unit; that meant a commercial job.
Ron
Interesting reading.
http://dcra.dc.gov/dcra/frames.asp?doc=/dcra/lib/dcra/information/forms_docs/pdf/dcmr12.pdf&open=|33466|
It is very difficult finding/navigating through DC government services. I can see your point now. At first glance it would seem you are under the 2003 IMC, but then I read where ASME & other regulations kick in. You have some silly rules down there, and if I can't put my finger on it , well, then,,,,,,,,,??
Nevermind............I think I'm gonna call Weezbo now, this is right up his alley! (just kidding Weez)
Robert O'Connor/NJ0
- 87.1K THE MAIN WALL
- 58 Biomass
- 115 Chimneys & Flues
- 111 Geothermal
- 163 Indoor-Air Quality
- 72 Pipe Deterioration
- 6.4K Radiant Heating
- 393 Solar
- 15.5K Strictly Steam
- 55 Water Quality
- 49 Industry Classes
