wiring, water feeder
hi, just would like to know the proper wiring for hooking up a model 101a mm automatic water feeder to a series 67 low water cutoff. ill use a sepeate 40va transformer, but dont what terminals to use on the water feeder. thank you tom0 -
You could try going online to the manufacturer of the water feeder for a wiring diagram.0 -
McDonnell & Miller
101A-24 and Series 67 LWC requires a MM transformer model 101-24V-48 first of all.
Power the transformer off the primary side of the system transformer 120 volt line following proper polarity.
Install the "C" (common) to one side of the water feeder from the water feeder attach the other wire to terminal 4 on the LWC.
Finally wire the "R" (hot) from the transformer to terminal 3 on the LWC.0 -