gypcrete and floor truss loading
Plumdog_2
Member Posts: 870
I see in my Maxxon Brochure (several different types of poured floor leveling, sound proofing, fire-proofing and thermal applications) the Therma-floor weighs in at 12lbs/sq.ft when applied at 1.25 inch thickness,or about 115 lbs per cubic foot. Gyp-crete is listed at about the same. I was curious to know because I recently worked a project where one of the radiant panels was 3 inch regular concrete poured over what I think were 16 inch TGI on 16 in. centers with 3/4 ply subfloor; about 24x30 feet.
gypcrete floor truss loading
would anyone know how many pounds per square foot you would figure for gypcrete with tile flooring , I need this figure for floor truss design.
thanks
Mike Terry0 -
Lightweight concrete
I imagine Gypcrete falls in the lightweight category, conventional concrete being 140-150 PCF with "lightweight" concretes at 110-115 PCF. To be sure I would get manufacturers data and consider the wet weight versus the dried weight.
Now to thickness, something only you would know: if say 110 PCF and 3 inches (0.25 of a foot) thick the weight would be 110 x 0.25 or 27.5 PSF.
(By comparison if all standard weight concrete, three inches would be 37.5 PSF).
Your thickness may well be less.
I usually figure tile and cement underlayment at the same density as standard concrete or stone. Often it is less but there is enough variation and the total when on a PSF basis for a thin layer is relatively minor. Say an inch of finish material (generous) at 140 PCF, 1/12th of that would be just under 12 PSF so my total with LW concrete and tile finish would be under 40 PSF dead load added.
Just keep your thickness in mind, get manufacturers wet data where you can, keep your deflections low (1:360 or better as may be recommended) and your pours small.0 -
Gyp
13-14 lbs per SF @ 11/2" depth.
- 87.1K THE MAIN WALL
- 58 Biomass
- 114 Chimneys & Flues
- 110 Geothermal
- 161 Indoor-Air Quality
- 999 Plumbing
- 391 Solar
- 55 Water Quality
- 45 Industry Classes
