Window heat loss
jp_2
jp_2 Member Posts: 1,935
> Radiant heat transfer is just that- "radiant" and <BR>
> not "conduction". "Transmission" heat loss or <BR>
> gain is normally only via conduction. It all <BR>
> depends on how window manufacturers express their <BR>
> catalogue performance data. The "U" value is a <BR>
> thermal resistance value which is based primarily <BR>
> on conduction of one temperature on one side of <BR>
> the window to another temperature on the other <BR>
> side of the window. The normal heat loss and <BR>
> heat gain estimates use the ambient air <BR>
> temperature on one side of the glass to the <BR>
> other. But the missing gap is that the actual <BR>
> temperature of the glass surfaces may not be the <BR>
> same as that ambient air temperature, so you can <BR>
> have some fairly high differences in actual total <BR>
> heat transfer when the radiant component is taken <BR>
> into account. <BR>
<BR>
  • Patrick North
    Patrick North Member Posts: 84
    Window heat loss?
    Anyone have opinions on performance differences between interior versus exterior storm windows?
    Thanks,
    Patrick
  • Mark_46
    Mark_46 Member Posts: 312
    Patrick
    To be honset, never even heard of interior storms. Can you explain?
    I currently have the 'ol triple track types on my house (already installed when bought house) I will soon replace storms and windows with replacement windows, etc. But the storms do a decent job of cutting down wind draft. Or at least keep the old wooden sashes from flat out falling out of their openings :o). Just kidding.
    Aside from old triple tracks, I have seen more modern day strom windows that I'm sure way outperform stroms of yester-year.
  • Patrick North
    I believe they're generally meant for situations where it'd be inconvenient to use exterior versions- like large third story windows.
    I was thinking that since the outside pane can't be airtight (trapping moisture) and the existing windows are anything but, it might make more sense to use interior storms that can be fitted quite tight.
    The windows in question are oddball sizes and configurations that won't lend themselve to the permanent triple-track type storms.
  • Constantin
    Constantin Member Posts: 3,796
    They have their place...
    ... interior storms can frequently be found in historic districts where local zealots demand old windows not to be obstructed by modern storms. Thankfully, our historic commission is more concerned about the welfere of the original windows than the storms that would protect them.
    The biggest issue I have heard of when it comes to interior storms is condensation. While that can happen on the exterior storm as well, it's easier to drain the condensate out there, where gravity, etc. can do their thing. On the inside, the condensate can lead to rot.
    Now, if the windows and frames were air-tight (unlikely) then perhaps the condensation issue would largely go away. But windows being windows...
  • Brad White_9
    Brad White_9 Member Posts: 2,440
    All the same...
    The issues of storm windows and condensation are related to how well the inner window seals, whether the prime window or an inside storm. So if they seal well regardless it does not matter what you call them.
    Heat loss: Same concept. All of the heat loss (talking transmission here) is in series through the materials, essentially regardless of order.
    If your prime windows are single pane glass and you have interior or exterior storm windows, you still have two panes of glass plus a theroretically dead airspace between. The thinner this airspace the better it works because there is less volume for convection within that space.
    If one of the surfaces, specifically the (IIRC) No. 3 surface (inside face of the outermost pane) has a low-E coating so much the better. Low-E aside, the series heat loss, inside to outside, reads like this:
    1) Interior Air film; R-0.68
    2) Inner Glass; R-0.16, negligible really.
    3) 3.5 inch Dead airspace one hopes; R-0.91
    4) Outer Glass; R-0.16 oh boy.
    5) Outer Air Film assumed 15 MPH wind; R-0.17
    Total R value = 2.08
    Total U value (1/R) = 0.48
    The realities of air leakage diminishes this somewhat. I was taught that single pane glass has a u-factor of 1.13 and that a single pane glass unit with storm window should have a u-factor of 0.68.
    With Low-E windows there is a caveat: Manufacturers list "center of glass" values, often in the 0.28 to 0.35 range. When averaged over the entire window unit, taking into account even modest thermal bridges at the edges where the glass comes together, the overall window u-factor rises to the 0.40 to 0.45 range in my experience. Absent manufacturer's adjusted data, this is what I use for low-E glass.
    Hope this helps.
    Brad
  • Patrick North
    Great-
    So if I'm unable to get a good seal with the primary windows, it's better (from a condensation point of view) to have interior storms- as long as they're tight, right?
    As an earlier poster quessed, this is a historical district situation, and in most cases the permanent tracked storms wouldn't have worked, anyway.
    Thanks,
    Patrick
  • Mike T., Swampeast MO
    Mike T., Swampeast MO Member Posts: 6,928
    The main benefit of interior storms seems to be aesthetics. If you use them, make certain that the actual sash are in top-notch shape and nicely weatherstripped.
    To open the window you have to remove the interior storm--and then you'll probably still need external screens.
    They do nothing to protect the original sash from the weather so they'll require more frequent maintenance.
  • D107
    D107 Member Posts: 1,911
    another timely post brad
    I'm winding up my own heat calc and the hydronic institute H-22 Guide I use lists double glass wood or vinyl windows at U .341 (low e's at .263) so maybe I'll rethink that.
    Thanks,
    David
  • GMcD
    GMcD Member Posts: 477
    And then factor in radiant effect
    What's also missing in the standard calculations for window thermal performance are the radiant heating and radiant cooling loads off the glass. As I've been trouble-shooting underperforming HVAC systems, I found that even a lightly tinted window in direct sunlight will experience the outer piece of glass (double glazed sealed units) getting up over 100F during a 70F ambient outdoor air temp. This temperature then radiates through to heat up the inner glass which can result in the interior glass surface temperature being around 85F to 90F. At an ambient indoor temp of 72F, that's an added 20-25 Btuh per Sq. Ft. of warm glass that is direct radiant heat. Reverse is true in winter- the inside glass surface temps can be down around 50F at an out door ambient of 15F, resulting in a lot of radiant cooling going on.
    So, yeah- what Brad said above, plus more glass thermal physics to keep in mind. The standard calculation of "just transmission" losses/gains through glass are merely an estimate, and not very accurate at that depending on the input information.
  • Ericjeeper
    Ericjeeper Member Posts: 179
    I personally would not waste my money on storms interior or exterior if you forsee new replacement windows in the next few years.
    When you get ready for windows , get a lot of prices..Lot of companies selling the exact same window at all sorts of varying prices.
    Around here some companies sell their windows for 900-1200 each installed,and it is usually the same window a smaller company will sell you installed for 500-600.
    New windows let a lot of daylight into a home that old glass blocks out..My customers are amazed at how bright their home is now.And all of them brag on the new comfort and appearance.BTW I sell and install Alside brand windows.
  • Brad White_81
    Brad White_81 Member Posts: 15
    Thanks for the excellent point, Geoff
    You being in the Great North suffer more from solar gain through vertical glass than do we below the 45th parallel :)
    Radiant effect is a low-E issue or better said, low-E coatings cheat the radiant effect and create an equivalently lower u-value. It does not change the surface temperature of the glass significantly hence does not truly effect transmission which is what most conventional heat loss calculations are about. (Or "aboot" as you may say, Geoff :) )
  • Brad White_81
    Condensation the where and why
    The general rule on condensation with storm windows is this:
    If the condensation occurs on the inside face of the outside pane, it points to the interior window being leaky. Moist interior air finds the colder surface on which to condense.
    If the condensation occurs on the inside face of the inside pane it generally points to a leaky outer window, allowing the inner window to cool below dew-point.
    So if your outer windows are so-so (as is your local Hysterical Society) then yes, interior storms are the way to go and sealed as well as you can.
  • GMcD
    Window equalizer software
    I use the Lawrence Berkeley Labs "Window" free download software to calculate "overall" U values and surface temps that are all calculated to NFRC Standards that can really open your eyes about the sales hype vs reality of window performance. Weblink: http://windows.lbl.gov/software/window/window.html
  • ttekushan_3
    ttekushan_3 Member Posts: 963
    Interior storms.
    > windows? Thanks, Patrick
    Terry T
  • ttekushan_3
    Interior storms.
    I've built nothing but interior storms, as the windows I've restored are all pre-wwII steel casement windows. Usually Truscon or Fenestra. The interior storm covers the entire daylight opening. Since the storm window is on the interior you can use acrylic since it won't see very much dirt, weather, and UV. On the interior, the acrylic won't yellow prematurely (at least 18 years before visible yellowing). I always recommend the scratch resistant coated acrylic.
    The acrylic's R value is better than glass, its much better at blocking UV, and it has better low E properties than glass. Particularly since I use 1/4" glazing with minimal framing, or no frame at all for moderately sized windows or smaller.
    The low carbon content of the steel used in those old casements can weather very well. The house I live in has these. As they were, they were intolerable to use, or live with. I used an aircraft lubricant on hinges and hardware, stripped most of the paint off with a razor (it was surprisingly easy), knocked most of the glazing compound out, primed everything with oil base paints, reglazed, repainted. Whew! Oh. and I made my own seals with caulk. Its really easy but no one thinks of it. But I did these windows 16 years ago and they are just now starting to chalk a bit. They are no worse for their wear after 68 years in the weather.
    Subjectively and objectively (thermal imaging) these windows are outperforming my neighbors' replacement windows. And the sound isolation is much much better also.
    But I agree, more fragile historic windows, particularly wood with lead-came inserts should get tasteful exterior storms.
    Terry T
  • ttekushan_3
    Interior storms.
    The low carbon content of the steel used in those old casements can weather very well. The house I live in has these. As they were, they were intolerable to use, or live with. I used an aircraft lubricant on hinges and hardware, stripped most of the paint off with a razor (it was surprisingly easy), knocked most of the glazing compound out, primed everything with oil base paints, reglazed, repainted. Whew! Oh. and I made my own seals with caulk (ask if you want details). Its really easy but no one thinks of it. But I did these windows 16 years ago and they are just now starting to chalk a bit. They are no worse for their wear after 68 years in the weather.
    Subjectively (comfort level near the window) and objectively (thermal imaging) these windows are outperforming my neighbors' replacement windows (with the exception of the ones with so many coatings and shadings that the interior of the house is downright gloomy. Could never live with that. I'll close the drapes at night for the same effect, thank you). And the sound isolation is much much better also.
    -Terry
    Terry T
  • jp_2
    radiant losses
    how can you seperate radiant loss from transmission losses?
    seems to me that when measuring losses the radiant loss gets thrown in, after all its all heat loss.
  • GMcD
    Basic physics
    Radiant heat transfer is just that- "radiant" and not "conduction". "Transmission" heat loss or gain is normally only via conduction. It all depends on how window manufacturers express their catalogue performance data. The "U" value is a thermal resistance value which is based primarily on conduction of one temperature on one side of the window to another temperature on the other side of the window. The normal heat loss and heat gain estimates use the ambient air temperature on one side of the glass to the other. But the missing gap is that the actual temperature of the glass surfaces may not be the same as that ambient air temperature, so you can have some fairly high differences in actual total heat transfer when the radiant component is taken into account.
  • Mark_35
    Mark_35 Member Posts: 44
    Interior Storms
    Check out Windo-Therm out of Hoosick, NY. They make a two layer clear plastic interior storm that stops pretty much all infiltration and has a very good R-value.
  • Mark_35
    Interior Storms
