repipe old CI radiators, My customer now has a new boiler
G Lyons
G Lyons Member Posts: 36
My customer has a new Dunkirk boiler and baseboard radiation in the addition to his home. He is heating the old part of the house with the original cast iron radiators, which he likes. I would like to repipe the radiators so as to get rid of the large volum of water the pipes hold. How should they be piped. Can I pipe them in series as the baseboard is done, or will I have to use monoflow tees. There are only 6 old radiators to pipe to. I hope not a supply and return from each radiator. Help Please.
  • Mike T., Swampeast MO
    Mike T., Swampeast MO Member Posts: 6,928
    With the possible exception of adjacent radiators in the same room standing iron should never be connected in simple series. If you must use one-pipe, then use monoflow/diverter tees. Two pipe systems generally give better control possibilities.
    If you connect them in simple series you will have terribly uneven heating.
    Don't forget that when piping a monoflow system you must size the radiation for the lowering supply temp after each radiator. An existing two-pipe system will NOT be sized with that in mind!
    While the big, old mains do hold lots of water, it's usually not a problem if you insulate the piping.
  • G Lyons
    Re; new piping to old CI radiators. Thank you Mike T.
    I see what you mean. I will leave the piping configuration the same but install 1" cu or pex in place of the large old iron pipe that is also taking up head room. I could supply and return from the large radiator with 1" and 3/4 inch the smaller radiators. Would that work?
  • kevin coppinger_4
    kevin coppinger_4 Member Posts: 2,124
    you know....
    if you set the system up as a manifold you could run a seperate line of 1/2" pex to each radiator as a supply and return.......kpc
  • jeff_51
    jeff_51 Member Posts: 545
    just a note
    CI rads and baseboard must be on seperate zones if you dont manifold or you will get very uneven heat
  • Dave Stroman
    Dave Stroman Member Posts: 766
    I use reverse return. No diverter tees needed and you can turn off or balance any number of radiators without interfering with the flow to the others.
    Dave in Denver
  • G Lyons
    Whats reverse return ? Thank you for the help.
    I can see that a header would work fine.. I will run 3/4 to the large rad in the living room and 1/2 to the other 3 rooms. There are 4 rads in all not 6.
  • Wayco Wayne_2
    Wayco Wayne_2 Member Posts: 2,479
    Kevin!
    You beat me to it. For several years now I have been replacing large gravity pipes with a manifold and 1/2 in PEX. I usually use Multicore for this. People around here on the Wall refer to it as a "Home Run" system. Homeowners love to get more ceiling space in their basement. (especially the tall people, clank!.. Doh!) Most want to finish off the space for a play room of some sort. I use Wirsbo Brass manifolds with the flow sensors so I can balance the loops separatly. It's easy to run the pex up into a joist bay out of the way. I usually set them up for constant circulation too. Bring the constant circ loop on with an outdoor stat or tie a relay into the B terminal on the sub base of the House tstat so that when they switch to heat it turns on the circ. :P WW
  • Constantin
    Constantin Member Posts: 3,796
    Sometimes, a picture speaks a thousand words...
    ... see below. Basically, reverse return ensures that each circuit gets about the same amount of water by making all the flow-resistances as similar as possible. Naturally, this works best for manifolds where all the attached piping is the same length, etc.
  • G Lyons
    Revers return
    Thank you Constantine, for the reverse return primer, I have heard this called "first in last out" and used on water heaters and softeners when installed in a bank (group).