Leak from Indirect?
Tony_23
Tony_23 Member Posts: 1,033
Check the sensor well connection. I've had one leaker that didn't show up until it was heated. Pretty hard to get condensation from that style, being tank-in-tank.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=384&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
  • Walter_3
    Walter_3 Member Posts: 20
    Leak from new Indirect?
    Guys, I need help.
    I have installed new indirect water heater. It was under the pressure over one week. The boiler wasn't completed at that time, but was also under pressure. When I started the boiler I got wet floor under indirect water heater I've checked all the connections and could not find the leak. It looks as if it is coming from the bottom of tank. Could it be some condensation? I am running out of ideas, please help.
    All the best,
    Walter
    PS. Pictures are attached.
  • Brad White_9
    Brad White_9 Member Posts: 2,440
    One way to find out....
    If you are certain of your connections, isolate the indirect on both inlet and outlet. Let the tank cool to ambient or force it to ambient to minimize T/P relationships.
    Put a gauge on the drain valve and see what the pressure does overnight. (Should I say Overknight? Nah. Too easy.)
    No change or within range of any temperature change? Condensation. Definite drop in pressure? Houston, we have a problem. I would still check the connections before further steps.
  • water leak
    Pull top off tank and check for leakage at sensor well at top of tank .They have a kit to replace o ring .