Circulator operation
Brad White
Member Posts: 2,399
Understood, how could one resist? Still, and as you know, we have to respond to these questions on the basis of what is available....
did I say that? <i>"What is available..."</i>
Yes. Yes I did.
Yes. Yes I did.
"If you do not know the answer, say, "I do not know the answer", and you will be correct!"
-Ernie White, my Dad
Which is the best way to operate circulators?
1. Constant-running circulator, in which the pump is controlled by a manual switch. The pump is usually turned on at the beginning of the heating season and runs constantly until it is turned off at the end of the heating season. The boiler is independently activated by the thermostat as heat is required.
2. Aquastat-controlled circulator, which turns the pump on and off at a preset boiler temperature (normally 120 F. Like the constantly running circulator, the burner is independently activated by the thermostat as heat is required.
3. Thermostat-controlled circulator, in which water is maintained at a constant temperature in the boiler by an aquastat.
4. Relay-controlled circulator, in which the pump is activated (via a relay switch) whenever the boiler is activated by the thermostat.
Thanks for all replys.0 -
Hi Roger, what type of emitters are you using? Condensing boiler? Outdoor reset? Trying to get by for the lowest cost or looking for the highest comfort level?0 -
Will you accept \"It Depends\", Roger?
In order of your choices:
1) Constant running via manual switch (or outdoor T-stat I will add): Fine if this is the secondary/radiation side of things or if your boiler has low temperature protection or is a condensing boiler.
There is a school of thought that constant circulation with TRV's on the radiators and the boiler fired by the thermostat give a "by-default outdoor reset", with warmer temperatures in cooler weather. A minimum or low boiler limit is usually required unless it is a condensing boiler.
2. Aquastat control: Fine if you have no other boiler low-limit protection. This is a traditional way to control a lot of boilers since the 1940's-50's. Wastes energy as you are firing the boiler while delivering bupkes.
3. Thermostat-control with constant boiler temperature: Best way to control any system if you are a gas or oil companyLarge cycles in space temperature, arbitrary fuel consumption, one flavor all the time. At least add boiler outdoor reset to keep a range of 140 minimum up to design high temperature.
4. Relay Control in parallel with boiler. Provided you have boiler low limit protection, this is probably the smoothest compared to constant circulation. No big inrush of hot water as with constant temperature.
Best of all worlds in my opinion: Circulator run off of OD temperature below say 65F. 4-way mixing valve with outdoor reset and boiler protection (if a conventional high temperature boiler) or direct modulation (if a gas fired condensing boiler) for a simple one-zone system.
Best combination of indoor temperature comfort and energy savings.
My $0.02
Brad"If you do not know the answer, say, "I do not know the answer", and you will be correct!"
-Ernie White, my Dad0 -
4 way puzzle?
brad why the 4 way mixing valve with OD reset and a modcon?
got a diagram?0 -
Not with a Mod-Con
There are so many variables with these hypothetical intances, JP-
I would never use a 4-way with a Mod-Con. A 3-way if I needed a zone mix-down but otherwise straight off the Mod-Con if I could.
For a conventional cast iron or high temperature boiler, I prefer 4-way valves for all the right reasons."If you do not know the answer, say, "I do not know the answer", and you will be correct!"
welll
I guess if i would read your post closer I wouldn't ask a dumb questionnow I see the errors of speed reading.
Evelyn Wood
never read the word "hydronics", even slowly."If you do not know the answer, say, "I do not know the answer", and you will be correct!"
Circulator Operation
These are all great comments for standard, constant speed circulators.
The newer technology ECM VFD type of circ controls itself (automatically decreases speed and flow as zones close). Even with a no flow requirement these residential circs draw less than 6 watts - can run at zero flow (deadhead) forever without overheating. These have been available in Europe for quite a while and larger ones are currently available over here - smaller residential types will be available soon.
In saying that, for optimum energy savings it might be a good idea to automatically shut these off during warm weather shut down.
Appologies, couldn't resist.0 -
variable speed pumps
Hi Steve, When do you expect those new residential pumps to be available over here? I'd be happy to have my house be a test bed0
- 87K THE MAIN WALL
- 116 Chimneys & Flues
- 107 Geothermal
- 983 Plumbing
- 389 Solar
