tx valve
will smith_4
Member Posts: 259
A txv is adjustable so you can set it up to maintain a desired amount of superheat. Compressor manufacturers will tell you how much superheat is required at the compressor for optimimum performance and protection. It's fairly standard to see a 10-15 degree superheat, though some want as much as 35. Once the system is stable and your superheat is set where you want it, you shouldn't have to touch it again. Make sure your bulb placement is correct, secure, and well insulated. Unless someone has played around with it, the txv is basically set and forget. I'd apply some leak lock at the stem cap on that leaker-
tx valve
Is it normal for refrigerant pressure to come out the bottom of a tx when you remove the cap to adjust superheat0 -
Sometimes there is a set you can tighten at the point of ajustment,otherwise tighten cap to pervent leak lockleak may help0 -
HUH?I went to lossen the cap to adjust superheat and pressure and dripping refridgerant came out.Iended up pulling into sucback adjusting evacuating then opened system,My question was is this normal?0 -
TXV
Hi! Was the TXV working properly, other than needing a slight adjustment?0 -
txv
You should not expect a leak at a txv adjustment stem any more than you would expect a leak at any service valve. If the valve leaks and tightening the packing does not stop it, it has incurred damage (probably by being overheated when it was installed)-and should be replaced.0 -
Definitely NOT Normal
This is definitely NOT normal.
One question, though. The TXV has a one-line job description, which is to maintain constant evaporator superheat. Prior to your attempting to adjust it, was the valve maintaining superheat? If so, why are we adjusting it?
If the TXV is not maintaining superheat, adjusting the spring pressure is not going to correct a mechanical problem with the valve.
Actually the tx was union type and installed after brazing so it was not overheated.The valve was a Lennox and had a one to three ton rating.I was installing on a 2.5 ton. On first start up superheat was at 20 and I was trying to bring to 10.I was told to adjust because the tonnage flexablity of the valve.Please correct me if I am wrong.Thanks0 -
Just be VERY Careful
When adjusting the TXV make certain that you turn the adjustment screw in SMALL increments at a time (0.5 to 1 turn), and be sure to allow the system to operate for at least 10 minutes between adjustments. Make certain that you repeat your superheat calculations before each adjustment.0 -
Hay curiousity kills
On any "start-up " the superheat is going to out of bounds for awhile,then once the system is stabilized an accurate superheat can be taken and adjusted.Enjoy!0 -
Thanks for the responses but my original question was is it normal for pressure to come out when removing the cap0 -
Just Courious
As The professor said -NO- .but I'm still courious about the superheat adjustment!0 -
well then why is it there if you dont touch it
if you get pressure when removing the cap
There is a leak in the valve-replace it.0 -
Courious
It's there to be touched,BUT,BUT,BUT,from what to what?0 -
It's not surprising to find that the valve leaks... some more than others.
Make sure the nut is tightened so the leak is contained at the stem and not escaping.
Curiosity does kill... and in HVACR it's usually the compressor.
good luck
thanks for the response
> leaker-
So....
So txv manufacurers can sell a lot more valves when people adjust them when they shouldn't. The saddest part of the whole thing is that if a technicians does not know how to properly adjust a TXV they an successfully kill the compressor.
Just remember..... Small adjustments.... wait 15 minutes.... make superheat calculations...
No race..... take it slow.... nice and slow....0