Heat Loss/Convector Question
Options
Dan_15
Member Posts: 388
Hi, I'm trying to do a heat loss for a room that is somewhat cold in the winter. If I've done it correctly, the Slant/Fin Heat Loss Express program tells me that I have 6,410 BTU/hr heat loss in the room. Now I need to find out the output rating for the finned/tube convector that is in that room. It is a 4 foot long unit. It is stamped with the name Tuttle & Bailey, and it looks like there are three-pipes surrounded by fins, and a tall bleed valve poking up the side. Also, the entire convector was retrofitted during a remodeling project so it no longer has the same characteristics as originally installed. During the remodel, it was fully recessed into the wall and cut down by about 3-4 inches, which reduced the cavity of air above the fins a bit. The metal cover/housing was removed, and it is now housed inside an insulated wood frame with a metal grille. What would this have done to the output rating? Also, do you think that lining the box with reflective bubble foil would affect the output rating? Thanks, Dan
0
Comments
-
Dan
I'm not sure what the ratting on your existing convector is, but at 3/4" feed to the convector you can expect 600BTU per linear foot base on a 180* average water temp with a 20* drop. By putting it in a recessed wall, I would think that you are killing the air draft that is created as the warm air rises. I think the best thing for you to do is find a Pro in your area that can look at what you have and make a recommendation as to what's best.
Mike T.0
This discussion has been closed.
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements