staple-up radiant heat
Ron Gillen
Ron Gillen Member Posts: 124
Just search - Author: Gary Hydock and you'll see where he's coming from. He's advertising an above the floor system.
  • michael_30
    michael_30 Member Posts: 2
    staple-up radiant
    I have an oil- fired hot water boiler, with a summer/ winter hook up. My supply comes off the boiler into my flo-check,from there it tees one side goes into my expansion tank, and the other side goes and tees off into 3 zones,(i have no zone valves.)All 3 lines loop back and tie into the return, then into the circ, and into the boiler.I cut out my first floor baseboard and installed onyx tubing. My plan was to tie back into the zone I cut out. From my supply on that zone into a strainer,then a flo-check into a tempering valve then into a circulater and then into my radiant coming back with a check valve and then into my existing return. Will this work?
  • kevin coppinger_4
    kevin coppinger_4 Member Posts: 2,124
    are you just...
    Pump away from the mixing valve...never into it. Did you do a heat loss? kpc
  • michael_30
    Yes, I did a heat loss, and my circ is after the mixing valve. I was told, if my bedroom zone was calling for heat and the radiant zone wasn't there could be a problem or vise versa.
  • Steve Garson_2
    Steve Garson_2 Member Posts: 712
    You're going to need zone valves, since the heat demand with differ from the basement to the rest of the house.
    Steve from Denver, CO