GB142-24 Required Flow
Steve_35
Member Posts: 545
but I can't find in the install or application manuals the required flow rate for the GB142-24, the head at that flow or a pressure drop chart. I'm pretty sure Buderus makes that info available, I'm just not finding it.
We're installing this on a job that already has an indirect WH. I just want to make sure the DHW pump is sized correctly.
I tried e-mailing Joe but apparently he's out of the office till next week.
Thanks.
Thanks.
gb
Its definitly in the applications manual, pages 2 and 3.
It comes pre plumbed with its own boiler pump...
You just need to worry about the flow requiremnts and head for the system...
Purdy fart smellers them there Buderi fellers are....
ME0 -
I don't think the boiler pump runs
on a DHW call.0 -
dhw
No the boiler pump doesnt run for dhw.
EDIT: found it. look above.
These charts are for Buderus indirects.
We have a SuperStor. Thanks anyways though. I'll give Buderus a call this am.0 -
Grundfos pumps
I can't wait to try out the new 3 speeds,(26-99fc) they cover a lot, perfect for this application.
I can't fine the pressure drop of the GB either, just the reccommended pumps for their indirects.
Spoke with Buderus this am.
The GB142-24 minimum flow is 8gpm at 8ft head. Makes it easy to remember.0
- 167 Indoor-Air Quality