80% Flue Temps
Jim Davis_3
Member Posts: 578
Flue temperatures should be proportional to what we are heating and in the case of 80% furnaces plenum air should be at least 130 degrees. We use a 170 degree added to air water or steam temperature on 80% equipment. 300 to 400 degrees would be the maximum ranges for 80% furnaces. Under 300 you are underfired over 400 you probably have poor heat tranfer caused by airflow problems.
These are high fire temperatures. On two-stage if the flue temperature gets much below 250 degrees some of the flue gases will probably cool and condense before they get out.
Boilers would run higher. Forget the DOE chart!!
I know that many things affect the flue temps on a 80% furnaces such as connector lenght, chimmney heights & types, BTU of unit and gas, Blah, Blah, blah.
But, can anyone give me an approximate flue temp range of a 80M, 80% N/G furnace?0 -
usually
about 300-425°F..ballpark.
Mitch0 -
Combustion Efficiency and Flue Gas Temperature
See attached.
Proper combustion tune-up to control excess air are important factors.
Doug0
- 120 Geothermal