Boiler pump placement on parallel P/S two-boiler system

Rocky_2
Rocky_2 Member Posts: 89
Can I place the boiler pumps on a parallel primary/secondary system on the individual boiler returns? Usually I put them on the supply outlet, but I am using two Buderus SB615-640 Mod/Con's and the centerline of the outlet is already about 65" high. By the time I get a Grundfos 50/240 pump and B&G 4" Triple Duty valve and a 4" ball valve all stacked vertically on each other, I will be almost above the ceiling. Am wondering if I can put the pump and triple valve on the boiler returns instead? What say Ye?
Warm regards from soon to be chilly Fairbanks.
Rocky

PS. I installed a Buderus 515-12 with a Riello RL50 last week. That is one SWEET system! 1.8 million BTU's running so quiet I can whisper sweet nothings to my honey on my crappy cell phone standing right next to the burner. Second identical boiler and burner goes into the system next week.