viessmann vitodens 100 dhw
Ted_9
Member Posts: 1,718
How is it piped?
I have a problem with a vitodens 100 8-24 kw.
Central heating works fine but the DHW keeps going hot and cold all the time. Could this be the DHW temperature sensor?0 -
The
100 has no integral control.
DHW Problems
The DHW problems may not be the fault of the boiler. The Vitodens 100 that you have is only told to turn on. You need to look at something other than the boiler0 -
It was the heat exchanger blocked up with crap0 -
Must have been
an awfully long year of cold showers.