Boiler Demand Control
Options
Gary Jansen_2
Member Posts: 26
Tekmar 260. Outdoor reset, wwsd, pump output, boiler control
0
Comments
-
A small hot water system with 24V valves at fintube and a constantly running system pump. The boiler control will provide outside air temp reset 9the boiler control will be based on the system temperature). I need something that will start the main system pump and activate the boiler lets say when the outside air temperature is below 65 deg (this is a small commercial building). I don't think the boiler control will do it (Lochinvar KBN).
Also I think it will work better if the boiler control temperature sensor is in the return instead of the supply. I am worried about short cycling the boiler. Does this make sense?0 -
reset
Why not use an indoor reset. It will be a better idicator of real heat loss, and not short cycle your boiler.
www.Exqheat.com0
This discussion has been closed.
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 427 Carbon Monoxide Awareness
- 119 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 165 Indoor-Air Quality
- 3.7K Oil Heating
- 76 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.6K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements