Boiler / hot water circulation problems
Options
john torhan
Member Posts: 1
I have a 4 zone hot water boiler with a series loop system.
3 out of 4 zones are ok. The 1 zone that has the problem has a Taco VRTX200-3 air seperator located after the pump on the supply, the other 3 zones do not have an air seperator. On a call for heat the pump is energized and my pipes are warm to the pump (180 deg water in boiler @ 16 psi), luke warm across the pump, and cool at the outlet of the air seperator. When I remove the plug at the base of the air seperator (bleed it if you will) I get heat to my zone. This is an intermittant problem. Any thoughts?
Thx.
3 out of 4 zones are ok. The 1 zone that has the problem has a Taco VRTX200-3 air seperator located after the pump on the supply, the other 3 zones do not have an air seperator. On a call for heat the pump is energized and my pipes are warm to the pump (180 deg water in boiler @ 16 psi), luke warm across the pump, and cool at the outlet of the air seperator. When I remove the plug at the base of the air seperator (bleed it if you will) I get heat to my zone. This is an intermittant problem. Any thoughts?
Thx.
0
Comments
-
hot water heat - circulation problem
I just bought a 1930's home w/ the original hot water /boiler heating (one pipe) system. The problem I'm having is getting the pump to circulate the "hot water" I'm pretty certain that the pump works, however, when the switch for the pump is on the burners shut off. If the switch is off the burners stay on and heat the water. What is going on ????? I'm definately new at this!0 -
Hey Byron- Deja Vu or what?
Ahem.
A number of things and without a photo of the boiler and near-boiler piping and controls, all one can do is guess.
You say "one pipe" so I will assume a monoflow or series loop system, hot water and not steam. Is this correct? Let us assume it is hot water.
It may well be that the pump operation and boiler firing are coincidental. The boiler may fire based on an aquastat and the pump may run on an aquastat of it's own. Is the cause and effect of switching the pump on and off and the boiler going on and off absolute? Or is it "sometimes"?
For example of typical operation, the boiler aquastat, in it's simplest form, only wants to maintain the boiler at a fixed temperature, to make domestic HW or to heat the house; regardless.
The pump on the other hand wants to operate based on your space thermostat calling for heat but it also may have in addition to this an aquastat that keeps the pump from running of the boiler is below a certain temperature. This ostensibly is to protect the boiler. Old hat, inefficient but for the 1930's it was all the rage.
I would find a professional, either a heating contractor or an electricial familiar with boiler controls. This could be messed-up wiring, crosses (mis-matched) setpoints, any number of things.
After all of this, it may well be a one-pipe steam system with a below the waterline hot water zone. Another situation that would still require a pro if you have any doubts whatsoever.
My $0.02
Brad0 -
Switch
One rather obscure but potential cause would be an on-on switch being installed rather than an on-off switch.
A more likely scenario would be improper wiring of the system, which can only be determined by a heating professional. Either way, you should call one.0 -
You really should
post this as your own thread rather than "piggy back" onto another poster's thread. You will get your own set of responses too!
Go to the "Questions" page ("The Wall"), click "New Topic" in the upper right, and paste away.
Cheers!
Brad0 -
Winterizing boiler
I have my house up for sale, and will be moving the first of the year. My question is if I turn the water, gas, and electric off, can I do anything to winterize my boiler so the water does not freeze in boiler?
Any helpful hints much appreciated.0 -
You really should
post this as your own thread rather than "piggy back" onto another poster's thread. You will get your own set of responses too!
Go to the "Questions" page ("The Wall"), click "New Topic" in the upper right, and paste away.
Cheers!
Brad0
This discussion has been closed.
Categories
- All Categories
- 87.4K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 167 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements