building a thermal trap
Met with a customer today that is getting a little "ghost flow" through a few areas on a huge geothermal job. He installed a thermal trap on the supply line to a coil. Does the distance of horizontal pipe between the drop and the rise back up affect the trap? I was taught to keep these as close as possible. Opinions?
  • hr
    hr Member Posts: 6,106
    Look at
    Siggy's December 05 article "Harvey's Horseshoe" for a good explanation nof the how and whys. I've had limited sucess with thermal drops, personally, but I did miss some of the fine details.
    Is a soft seat spring check out of the question?
    hot rod
  • Joe_75
    Joe_75 Member Posts: 57
    I think that the rise is key. I have used them on steam cond. wells but not in a hot water system. I think that at least a foot of drop and rise would be sufficient.
  • bob young
    bob young Member Posts: 2,177
    twenty-seven inches
    The heat sink we use on holby mixing valves is 27 " and has worked well for close to one hundred years.