Who's right???
andy_21
Member Posts: 42
Getting estimates on a new Direct vent Gas fired cast iron w/ outdoor reset, heating system for 3000sq'2 1/2 bath new construction home.
1ST fl. Radiant w/Hydro air back up, 2 nd fl Hydroair& 60 gal Indirect domestic hot water w/ prority.
Did the slantfin heat loss program & came up w/ 73K @ 0 design.From everything I read here, do the heat loss & size boiler to largest load. The heating contractor & plumber I met with want to go 120-130K. They say you need to account for the Indirect w/ at least 40K btu.
What they way to go?
I've stayed w/ Cast iron type because of the Different temp set up that we have, so I don't think the Mod/Con would help. Any ideas?
Btu for Indirect
You do not have to account for the btu's for the indirect as you should be using a priority control thus making it irrelevant...0 -
thoughts
I would size the boiler for the heat load, unless there is a particularly high domestic hot water load. Short-cycling is a very common problem, and there is no reason to deliberately cause it. Obviously I am completely guessing, but for a typical new home, 24btu/sf is an over-estimate of the heat load. I think you will find that the actual load is less than that, depending on the design of the house. Lots of windows, particularly high ceilings, or lots of rooms with 3 exposed walls among other factors will affect the heat load significantly.
You can size air handlers for reduced temperatures also. It is worth looking at a mod/con, particularly with a direct vent application. The mod/cons have the advantage of being compact, wall-hung, and sealed combustion, even without the efficiency gains, which you can still take partial advantage of with hydro-air.
The Vitodens 200 or 100 would be excellent choices. They do not necessarily need to be connected to a Viessmann indirect. The Triangle Tube Prestige is also a nice choice with a competitive price, though the smallest version is the 110.0 -
Consider
sizing the Hydro coils for a lower temp to allow for condensation for a good portion of the time and go with the Mod/Con.You only pay for the coils once. If you require more DHW than the boiler can recover go with a larger indirect and/or operate indirect at 160 w/ a Tempering valve(which you should have anyway)I'd keep looking for contractors
All three distinquished colleages are correct
Your "contractors" are playing it safe and not doing the math. Will they be paying your heating bill every month?
A Mod Con should NOT be ruled out. You reallt should get some quotes from the pros here at Find a Professional....The Best in the Business.....MaD dog
Yes.
> 3000sq'2 1/2 bath new construction home. 1ST fl.
> prority. Did the slantfin heat loss program &
> for the Indirect w/ at least 40K btu. What they
> way to go? I've stayed w/ Cast iron type because
Yes.
Yes.
What they have said already is quite true. Even your own heat load number seems high. I have a 2,800 sq ft 1906 two story 9 foot ceilings down, 8 ft up, and 700 sq ft of glass and my load is less than 50,000btu/hr at -4F. Oversized, misapplied boilers are hugely wasteful, wear out faster, and reduce comfort. Also, in several areas are against code. The one caveat for your installation is that I would increase the capacity some in order to make up for the typically 20% extra loss due to forced air ductwork.
Boilerpro
- 167 Indoor-Air Quality