pipe size
DanHolohan
Member, Moderator, Administrator Posts: 16,687
the <a href="http://www.heatinghelp.com/pdfs/281.pdf"target="_blank">B&G Handbook</a> in the Libaray (It pays to wander off the Wall), but I'm not sure you can do this with a loop that long.
Retired and loving it.
pipe sizing
what is the proper pipe size for a monoflow system that has a 85' loop. the boiler is 75,000 btu input. there is 65 feet a baseboard element. thanks.0 -
is this a test?
i hate Tests...
if you are talking about convector type baseboard heat
or iron baseboard Dan Has a great place on the site so you can take what you have and match it with what you need..i have something that i could send you that might be real interesting it simplifies things for you the installer...
this is a great place ... this is in Dans library...0 -
Is splitting the loop an option?
For a loop half as long and with a similar load, 1-1/4" would be my choice, but I agree with Dan, that 85 feet may be a tad long.
The other factor is, how many radiator feed sets? If you have only five large ones that is one thing. 65 one-footers makes for a challenge :P
Also, 65 LF of baseboard versus that 75 MBH boiler, I suspect some form of decoupling and reset would be of benefit.
Carpe' Opportunitas0 -
Purpose
Not saying you shouldn't do this but why are you doing it. Typically monoflow systems were used to allow individual control of radiators using thermostatic valves. Is this 65ft 1 big room??0
- 167 Indoor-Air Quality