Under slab insulation
marc
Member Posts: 203
There will be complete R-10 vertical edge and under slab insulation.
Marc
Marc
Builder inquired about the location of the R-10 insulation in relationship to the slab. He would like to install the horizontal insulation +/- 30" below the slab, in lieu of directly under the slab. Do you think it will effect the heating system in anyway? I think that at start up in the fall there might be a longer "lag" time until the room gets to the target temperature.
Thanks,
Marc0 -
I believe your on target
The purpose of the insulation is to minimize heat transfer in a given direction. By putting the insulation so deep, you are allowing the heat energy in the slab to be readily absorbed by 30" of some dense medium - I'm assuming dirt.
Every time you want to heat or cool that slab, the response time will be extremely long. In fact, I would venture to say, it would react as if there were no insulation at all.
In my opinion, the insulation should be directly under the slab to minimize the absorbtion of heat energy to the earth. In addition, your should have edge insulation for the slab to prevent heat energy from conducting out the sides.
+/- 30\" below slab?
What`s that gonna do for your comfort? Warming the fill in between. Do you want to pay fuel bills to heat dirt?
Dave0 -
why does he...
want it so low? I agree that this is not a great plan..if the sub soil is prepared properly the strofoam should support most any weight under that would be on the slab...kpc
It would depend
on how well the fill material conducts heat. A backfill of all pea gravel for instance would be a poor conductor. Dirt or clay a better conductor. Moisture content also wouyld be part of the equasion. A complex thing to model I'm told.
Regardless I would still keep the insulation layer under the slab pour. It's a hrd thing to correct if done improperly
hot rodBob "hot rod" Rohr
Living the hydronic dream0
- 85.7K THE MAIN WALL
- 49 Biomass
- 72 Chimneys & Flues
- 92 Geothermal
- 149 Indoor-Air Quality
- 3.2K Oil Heating
- 59 Pipe Deterioration
- 847 Plumbing
- 5.8K Radiant Heating
- 372 Solar
- 14.5K Strictly Steam
- 50 Water Quality
- 48 Industry Classes
- 15 Recall Announcements
