Radiant Heating Issue
ALH_4
Member Posts: 1,790
That carpet is a killer. You will probably have to run those north-facing carpeted zones hotter, which at this point probably means running the entire house hotter. You could also add supplemental heat with panel radiators if you have any access to the piping, which does not sound possible from your description.
I'm not sure I understand the control strategy. Why run a condensing boiler at 160 and mix it down?
Question?
The company I work for installed radiant in floor heating in a 6,500 square foot house in 2005. This winter we are having some issues with heating. We are in the northeast corridor of the United States and our design conditions are 15 degrees outdoor temp. with a 20 mile per hour wind.
The entire system was designed off of Wirsbo ADS without any red flags for secondary heating.
The whole project only requires 66,069 BTU's with a maximum water temp. of 129 degrees. The complete instillation excluding the basement and garage are in a gyp. over pour. Every room in the house is maintaining 72 degrees except the Master Suite (which is located on the northeast side of the house) and a kids room (which is also located on the northeast side of the house). These two rooms only seem to be able to maintain approximately 66 degrees. Both rooms have carpeting with an R-value of 3.19 which WAS factored into the software.
The system is powered by a condensing boiler which is set to run @ 160 degrees and it is mixed down with a Wirsbo 101. With full outdoor reset. The side of the house where we are having the problem has a manifold with 4 zones and is zoned with telestats. We do have a 14 degree drop across the tubing in the floor of the master suite.
We are looking for any help in clues in locating our problem.0 -
10 btu/sqft ?????????????????
The 10 +- btu/sqft should have sent a red flag up. It is very rare for a project to have loads this low. My guess would be that the information that was input into the software was inaccurate. Run a new heat loss calculation.
Tim D.0 -
Tim D.0 -
Hmmmm
i agree with andrew, why run a mod/con at a high constant temp, then mix down?
could be reduced flow problem in those two areas?
129F seems real high to me? looks like your tube spacing is large. I prefer around 6" on center. I'm running 90F supply in gypcrete with 5F outside temp, 68F room temp, 74F floor temp, R19 walls with lots of windows.0 -
The project does have second stage hydro air which was designed at 160 degrees it just dosen't opperate off of this t-stat.
We reran ADS after the project was completed and rechecked everything and still no red flags! I can send you a copy of the ADS if you have the software.0 -
ADS said to use 12" on centers so that is what we did. We've had projects where it has red flagged us and we had to change our tube spacing. Just didn't happen on this one!0 -
emmitter area
Did you account for the monstrous insulators that are taking up floor space in the bedrooms??? The mattresses are no heat emitting areas. The king size beds are probable nice and toasty but block heat transfer to the rest of room occupants.0 -
carpet is the culprit
I don't think it's a problem with the radiant floor design. I think those north and east facing rooms have too much heat load to work well with carpet over the radiant floors. I would start turning up the reset curve on the radiant zones. Hopefully warmer water will make it work. I have seen carpeted zones where supplemental heat had to be added where it was screaming hot under the carpet and the room would not get over 60°F.
As Tim says (and he is an expert), the output of a carpeted radiant floor will not me much over 10 btu/sf.0 -
my first time
I did 12" on center my first time, didn't like the floors preformance, luckily the gypcrete wasn't flat enough.
tore it all out and started over, 6" centers, very happy....
luckily it was only a 235 sq ft addition.
most people here seems to agree on tighter spacing.0 -
The room is surprisingly open. The only placed it is chocked is beneath two 2 x 3 end tables. The bed is 6" off of the ground with great air flow and there is a chiar by the windows. They have two huge closets so there is no other furniture in the room.0 -
That's a lot of wall exposure relative to floor area with lots of corners. Did you verify that the actual construction met your design assumptions? Can the software even compensate for those angles? With such low btu/sq.ft calculations I'd almost consider those corners like tube fittings--they may be short but their effective length is much greater...
A 66F bedroom where the common areas are 72F honestly doesn't sound bad to me--in fact some people would prefer such...
With the carpet and assuming that all of the floors have the same supply temperature available, I think I would have tightened the tube spacing regardless of what the software said...
This also sounds like a "hybrid" system of true hydronics and "hydro-air". Are you positive that the hydro-air isn't "hogging" heat? Such is very possible if the occupants are using significant daily setback in the hydro-air zone(s).
I recall Hotrod having some serious experience-related issues regarding a hypothetical design that I posted here with carpet in the master bedroom. Something along the lines of, "The numbers might seem good, but reality is different."0 -
Andrew,
I really think the carpet is the culprit too. But the HO is freaking out and we do not know what to do.
We shot the floor while it was running and got a surface temperature of 73 degrees and the wall temp was 69 degrees. Therefore we where getting about 8 btu's a square foot. There is an area with granit and we shot that and we had a surface temperature of 85 degrees. The carpet is killing us
But what do we do???? ADS said it would work and we have to make this guy happy....0 -
zones
Are these rooms on separate zones?0 -
Mike,
We factored every nook in this room when we reran the calculation. The walls where six inch and insulated with R-19 and the ceiling had R-30. They put R-19 below the floor. They do not set back at all and I have only seen the hydro run in the fall. I was there when it was 9 degrees out side and this was the only zone on the whole first floor calling. Everyone else was satisfied at 72 degrees.
The HO also thinks his fuel bills are too high but insists on keeping the house at 72.
The area with granit was in the same room. It was in front of a fake fire place.0 -
options
The only option I see at this point is to adjust the curve on the Tekmar control.0 -
What Mike sez
Patrol the envelope and make sure it got installed right- cracks sealed, insulation properly applied, windows as spec'd or better. Then, as others have pointed out, go back to the calculations and make sure that realistic, correct values were used for the inputs - you DID use the "overall U value" for the windows, and not centre of glass, right? You did pro-rate the wall R values for thermal bridging if and where it exists, right? The infiltration values and vapour barrier values were "assumed" reasonably?
10 Btuh per SF is nice, yes it may seem low to some folks but if a high quality envelope and window system was used, that's pretty reasonable. I've designed a house in the mountains up here with a -20F winter design temp and it maxed out at 6 btuh/SF (Four element krypton filled Visionwall windows and 18" thick walls, etc.- nice when the owner's needs were driven by the needs for stable indoor climate for horribly expensive antique furniture)0 -
It was at 125 max and the room was 66. We changed it too 140 max and the room is at 66 degrres.0 -
Any reasonable way to add panel radiators with TRVs to the high-temp portion of the system? Even if an utter slave, (e.g. under the control of another thermostat and using an existing circulator) it doesn't sound like you need too much heat to "tip the scale". Calculate your deficit and then grossly oversize the panels. In other words don't assume that the supply temp will be that of the high-temp circuit--more like 90F or so... Even then I suspect that the panels won't be particularly large.0 -
2nd stage hydro-air??
You've got some excellent advice from other posters, which I certainly agree with. The problem is, that you've got to work with what you already have in the floor, and somehow have to figure out how to make the homeowner happy.
We have installed systems with the floor radiant being the first stage heating and then the ducted system (hydro-air, etc) being the 2nd stage of heat. The problem that could accompany this is that you could overheat in areas that are not experiencing the lack of heating. If that was the case, then an automatic zone dampering system, such as Arzel, could be utilized. The zones needing additional heating would then be the only ones getting more heat.
Another thing that might come under consideration would be adding radiant to the ceiling. Could the tubing be attached to the finished ceiling and then have another layer of sheet rock installed and finished out? They would only lose approximately an inch of ceiling height. John Siegenthaler has some great info on ceiling radiant and NRT Rob is a big advocate of it.
Tom Atchley0 -
i did a similar designe year before last....
except that the space that juts out, is all glass and is a dining room.
over a cif stand up "crawl" space. i put it on a separate zone and the kitchen on another. the kitchen sorta over extends into the area with a dish washer that turns L by that first window. I backwards L walk trough is tile as is the dining room. i had wanted to add a panel rad ,,,your going to probably best off with one . use your heat gun IF to locate the tubing and chip away at it until you can just drill the two holes...re do your heat loss and add the emitter where it can radiate like mad and get the best convection current...turn the temps back to where you had them..and dial the temp down in the panel emitter so you get the lowest temp fluid zooming through it...
honestly , i hedged my bet by running out two lines (Under the floor)despite the objection to having it under a dining room window...
i stuffed two pieces of 3/4" through the floor before the pour... that way i can glide the 1/2" thru there in a flash..they havent complained this year..or last.. well over 50 below last year..0 -
radiant design
shouldn't your outdoor temp design be at 0 degrees for the northeast0 -
radiant
shouldn't the load calculations be set to 0 degrees for the northeast at 25 btu's/sq ft0 -
Not according to ASHRA! And when we put 0 as our design ADS says we only need 139 degree water to make the system work!
Three words...
in-fil-tration...
OK, its only one word, but I suspect it's eating your lunch. Anytime you have a dwelling that can't keep up even when you are nowhere enar design condition, AND Tthe emitter is nearing is theoretical peak, suspect the one element that we have ZERO control over that has MEGA control over us, that element being INFILTRATION.
Pop for the $350 for a blower door test and eliminate that as a possibility. Especially if you have a duct system coming from unheated spaces (attic).
Been there, done that, walked away smiling...
ME0 -
I just put radiant ceilings in my home office...
OMNI directional at that!!
Now I get floor conditioning in the space above, and radiant ceilings in my office.
Second only to radiant floors for comfort...
As a side note on this guys problems, get someone in there with an infrared camera when its mildly cold outside and I'll bet you see some interesting things...
The technology is here. Use it.
ME0 -
Limiting factor of radiant floors
Mark I have to ask why people don't use radiant ceilings in the potential problem areas, where floor coverings, and furniture decrease output? You never know how much furniture or how floor coverings may change after the original installation.
Bedrooms in particular can rob some floor area output with beds, and furniture. Usually because the floor space to furniture area ratio is rather small in most homes. A 300 sq.ft. bedroom could lose 1/3 of its output to furniture, plus carpeting of r3
This to me is the beauty of ceiling radiant, more effective output area with less chance of being restricted.
Usually the restricted areas are under kitchen/ dinning tables, desks.
One other thing is why limit yourself to 1' spacings? other than being cheaper it really limits your potential output,and once put in you are bound to it. Easier to decrease supply temps than increase from a efficiency stand point.
I'm just a student so I'm only looking for answers through asking questions. So I'm not saying everyone is doing things wrong. I'm just looking at things from a different perspective.
Gordy0 -
because, your feel as cold as your feet!!!...
and your feet under the table are going to be ice coooo-eld!!!
as for this thread's issue - i see a lot of window area, get a sheer chiffon curtain in front of them to stop the natural convection, cause in radiant homes the temps are typicaly much less, and even a drop of convection will make you really uncomfotable - just had this "sit-shu-tay-shun" in a kitchen built in a an exposed extension, plenty heat in the floor - but needed the convection stopped0 -
Kal
Sorry Kal, I don't buy the cold feet with ceiling radiant. I have both floor, and ceiling radiant.
When it comes to hardwood or tile in kitchens, baths solariums, I agree floor radiant there is no better way to go. When in carpeted areas you don't get cold feet with ceiling radiant.
Covective currents will chill ya no matter the heat source though, and I will agree window treatments are a cheap r value to keep high glass areas at bay.
Gordy0 -
Parameters
The carpet R-value may be greater than what you had anticipated. The house may not have been constructed with the insulating value you anticipated. The furniture in a bedroom also hampers the performance of the radiant floor.
I am sure theoretically the system should work, but the real world is rarely equivalent to the theoretical calculations. The R-value of the carpet might be 3.5. This affects your design temperature significantly. I take most manufacturers' specifications with a bit of salt. I have seen output ratings for some dry methods of radiant floor installation that were obviously extremely generous.
Luckily you are close to the desired indoor temperature. many people would like a 66°F bedroom. You might have to run the radiant floors with a steep heating curve with a max closer to the 160°F the hydro air uses. It will cause other zones to cycle more, but what else can you do at this point short of adding supplemental heat?
work
The install looks good. Nice and neat.
Massachusetts
has anyone checked delta t of loops are those pumps the ones with built in check valves; flow is the train heat rides on check it good luck0 -
When you
calculated the R value for the carpet, did you account for the padding? and did they use the same stuff they told you they were using? or did they decide on the upgrade at the past minute because it is their master bedroom...
a few thoughts0 -
Great questions Gordon....
and unfortunately, not one that I have an answer to. You and I have experienced the comfort of radiant ceilings, and we agree that it is second only to RFH for excellent comfort, and typically at alower cost than RFH... I dunno. Maybe one of the pseudo hydronic psychologist can tell us why. Where's Doctor Brad when you need him:-)
It's not from a lack of trying to tell and sell people on the concept, but for some reason, when you mention radiant ceilings, people curl their lips into the EWWWwww position, wrinkle their nose and shake their heads no...
As for hihger tube density, it comes down to cost. WHen it comes down to a lower cost of operation, as dictated by higher fuel prices, and people start going to hihger efficincy products, like GSHP with limited temperatures of output, then it becomes REQUIRED and economics drops out of the picture. But given the opportunity to "turn it up", and use less tube, which direction do you think the typical person will go..
And thanks for asking the questions. That is how we ALL learn.
ME0 -
RC
I grew up with radiant ceilings. It rocked.0 -
Yes they do...and the colder it gets the more they rock!0 -
Blower door
Infiltrometer Blower door and an infared camera I have the blower door but not the camera . My guess is infiltration is high in that room,but I'm not counting out other comments made here.
Point is this there is NO and I mean NO such thing as anaccurate heat loss without a blower door period. If you don't know the infiltration than you don't know the heat loss.
Case in point I own a 1900Sqft shed dormer cape circa 1992 .
My client owns a 1900sqft cape circa 1992.
my cape has 7.8ACH per day,my clients has 23!!!!!ACH per day yet a heatloss on both homes would be the same without this info. however the real heatloses and heating costs are vastly different.
What is a Infiltrometer Blower door?0 -
Tubing layout approach
Looking at the photo of the tubing layout which is a nice job by the way. I will assume that the wall to the right is an interior wall.
Would it have not been a better approach to serpentine the tubing in the opposite direction to allow more of the supply end of the loop to bear the heatloss of the bay configuration?
This would also have allowed you to tighten tube centers at the bay, and space greater toward the interior. Stop that loop at the jog in the wall, then pick up the exterior wall to left with seperate loop as is, only tightening centers at the exterior wall, and increase spacing to the middle of room.
For give my crude etch a sketch. I know this does not help now, but your problem is also help in dealing with future installs to avoid these issues. Maybe the greater minds than I will have differing opinions.
Gordy0
- 86.7K THE MAIN WALL
- 56 Biomass
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 159 Indoor-Air Quality
- 69 Pipe Deterioration
- 945 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 43 Industry Classes