A look at steam efficiency - (was in boiler temp thread)
RonWHC
RonWHC Member Posts: 232
is, & will remain, a hands-on technology. Most younger folks have no idea that the beast in the basement requires TLC. Don't care how many, or how advanced, probe type (fool proof, really(?) devices you screw into the block: somebody better check the water line & blow the beast down once-in-a-while. That doesn't mean filling a 1 gallon paint can w/ water once a year. How many of today's generation can be bothered?
How many steamers were replaced last season because of homeowner, property management, or gummint agency, neglect. The guy I buy boilers from says about 80%.
Ex: We ran a weekend call (before Christmas) for a condo we used to service. New management firm & the main guy was out of town. We still had the key, so why not? 1,300 mbh LGB. Replaced a dead fuse, amprobed, replaced mudded up gage glass, flushed the 51, blew the boiler & return down. Performed routine safety checks.
Main guy called on Monday. What had we done? How much? What's a gage glass? Why did we change it? Why did we flush the LWCO & drain water from the boiler? How much did the unnecessary work cost? His boiler company serviced the boiler in the fall. They never told him about the need for those procedures. Why should he pay for the additional time & parts? The conversation ended amicably & he paid the bill. Unfortunately, that experience is more & more the rule, not the exception.
Make steam as efficient and comfortable as you can. And it can be both. The Achilles Heel of steam systems is the lack of proper maintenance & the those who can perform it. That will kill steam boilers in the USofA. Dang shame.
  • Dave_4
    Dave_4 Member Posts: 1,404
    From Christian Egli...
    I hope people don't mind - Christian's reply to my somewhat tounge-in-cheek post in the boiler temp thread got me thinking about steam system efficiency and I didn't want the discussion to get lost in the other thread.
    Here's Christian's post about equating steamer run time to equivilent supply temp for a hot water system:
    "There is more to life than numbers and how hot water compares to steam, but I don't know any better. :)
    To expand a bit on BC's numbers, he was at 212F for 7.5 hours, while the rest of the time the steam was flat. Stone cold radiators. (Note how this is drastically different from what hot water is - Most have posted water temperatures of above 100F, which in constant circulation, will have presumably been kept that hot all day long)
    While steam comes at 212F, this is not the average system supply temperature; oppositely, hot water supply temperatures are (within a bracket) the average values. Can we compare apples to oranges? Yes we can.
    BC's system ran for 7.5 hours. In his whole day, there were yet another 16.5 hours that ran cold, and steam goes cold and flat within minutes (this is a source of great efficiencies). We can now compute the average system temperature for BC's system, let's guess his home is at 68F (radiators under draughty windows would be colder yet).
    (212F * 7.5h + 68F * 16.5h) / 24h = 113F weighted average
    113F averaged supply temperature for steam is surprisingly low considering BC lives somewhere where it was only 6F. In comparison, Al also at 6F, reported 128F. (Technically, this 128 is more of an instantaneous morning number, and I'd expect the average supply temperature for the whole day to be lower, possibly 113, who knows)
    Steam heat grabs you by the lapel, gets you out of bed in the morning and shakes you until you're cooked. You feel the heat and it's addictive. At 113F, it certainly isn't crazy at all, just different.
    What is modulated in a temperature space in a modern hot water reset is equally modulated in a time field for hot air and especially hot steam. Same difference.
    Was this a good splash or what?"
  • Dave_4
    More thoughts and info on the system
    That's a great way to look at this, I hadn't thought along those lines before. I think the approach might need a bit of refinement after looking at the numbers. I think the main issue is that the radiators heat up a LOT faster then they cool down since the steam condensing inside is much more efficient at transfering heat than the convection/radiation of the 70 degree air in the room. Also, my boiler is way oversized for the radiation load (1/2 of the radiators in the house are off), and it definitely keeps pumping steam into the radiators quite a while after it stops firing judging by air vent activity.
    I currently have about 310 sq. ft of radiation turned on, or about 75mbtu/hr. At a 6 degree outside temp, my best estimate puts the heat loss at about 40mbtu. I don't have a high confidence in this calculation since there are several key areas where I don't know the nature of the insulation, if any).
    So, if I assume that the radiators are at 212 or 70 strictly depending on boiler run time, the heat input to the house would be 75mbtu*7.5/24 or 23mbtu/hr. This is also the same as saying that the radiators are at an average temp of 113 (310ft2*1.7btu/ft2/hr*43deg=23mbtu/hr).
    Now I don't think my heat loss is off by that much. I'm not saying it is impossible, but I'd be surprised if it was. The other thing to consider is that if I am only outputting 23mbtu/hr to the house, my system efficiency is right around 50% (1.39gph*138500btu/gal*.78eff*7.5/24=47mbtu/hr avg). This is much lower than I would expect from a well-running steam system. True, I'm heating the basement pretty well with the boiler jacket losses, but the mains and risers are all insulated. Everything I've read and heard on this site indicates that a steam system should be capable of far better than this.
    I think the key is in how slowly the radiators cool down to room temp. Damn it, now I'm going to have to set up sensors to log the surface temp of the radiators tomorrow when I should be working on my Geo system.
    So stay tuned, steam fans. If what Christian says is true, my overall efficiency is less than 38%! The steam system efficiency even assuming a 100% efficient boiler would be less than 50%! My gut tells me this can't be true, but I'll try to prove it tomorrow with some more data.
  • Dave_4
    Another piece of the puzzle
    This shows a little of what I'm talking about - there is a significant lag between the boiler run time and the radiators heating up the room. The bottom sensor is close to the boiler stack, basically any time the temperature is increasing the boiler is on (I have verified this with my hourmeter). The top sensor is at my thermostat (either it reads a bit low, or the thermostat reads high, it is set at 68F during the day).
    I highlited the boiler on times, you can see that the room temp keeps heating up long after the boiler shuts down. I'll try to get some radiators instrumented tomorrow and post the results.
    Also notice the nice rapid warm up from the nighttime setback - one of the things I love about steam.
  • Steamhead (in transit)
    Steamhead (in transit) Member Posts: 6,688
    It would be interesting
    to see that graph on a system where the boiler is properly matched to the load. Even better, on a dual-boiler ⅓-⅔ setup like Terry Tekushian did. Since you have so much radiation turned off, this graph shows the behavior of an oversized boiler.
  • ttekushan_3
    ttekushan_3 Member Posts: 965
    Cast iron radiation
    evens out the temp distribution time. Fast "charge" into the radiator, slower discharge into the room. Low temp hydronics match charge/discharge times. So don't forget to introduce a time constant for cast iron radiation with intermittent firing. The proof is that a 100% efficient boiler would somehow waste 50%. Reality is, that's obviously not happening. You're somehow eliminating from the equation all the heat eminating from the radiators after boiler firing has ceased.
    Heat exchanger manufacturers usually stipulate that greatest heat transfer efficiency occurs with high delta T's and high delta P's (temp and pressure differences). So analyzing the entire heating system from fire to heated space, steam does quite well, thankyouverymuch. Delta T from fire to water within the boiler is somewhat less than with forced hot water (in non-condensing mode-more on that later), but is extremely high at the heat transfer surface (interior walls of the radiator), typically (215-100)+latent heat. Steam's total heat is around 1,000 BTU/lb. Also, pressure drop is HUGE at the laminar surface at the point of condensation (don't forget that water drops in volume nearly 1,700 times in changing back from a vapor to a liquid).
    Thermal transfer properties of steam are nearly ideal. Low mass, low pressure, high thermal content.
    Once phase change is introduced (i.e. heating with latent heat) the formulas have to take into account the initiation, or priming of the process. In typical (non-vacuum induced) steam systems, the boiler must develop the POWER of distribution before the POWER of condensation can take over. This is why there's a pick up factor. The pick-up factor is a good indication of how oversized (and less efficient) the system can become once condensation is established in each of the radiators. Efficiency ratings hold this against steam systems, perhaps with good reason.
    "Good reason" because the problem can be solved so easily. Simply remove the required pick-up factor from the firing rate once steam condensation is established.
    It seems that when boiler efficiencies are rated (outside the application) this power factor is never considered. Sadly, neither do the boiler manufacturers consider it since we are not given the option of staged firing in the typical steam boiler. When I encounter commercial steam heating plants with just two stage firing, its shocking how much of the time is actually spent at low fire. The best is a comfortably oversized boiler with an adjustable low fire for field "dial-in" to match boiler output to radiation load.
    Having this over capacity at will is a wonderful thing, IMHO, since a modern steam heating system could be designed with radiators sized smaller than your region's outside design temperature would indicate. The steamer could kick back into high fire and selectively (based on outside temp) increase the pressure to increase the output of the radiators during extreme weather conditions only. You'd probably see this happen maybe once a year. The rest of the time you are enjoying lower energy bills. At the end of the season you'd be very far ahead. In the meantime all we can do with existing systems is balance them for similar effect, and lower the firing rate with either a carefully placed aquastat at a riser or main (a la Boilerpro, Gerry Gill, Steamhead) or carefully tuned vaporstats. And it works.
    Steam is competitive with modern hydronics because circulation is just what steam wants to do naturally, and is naturally attracted to the coldest surfaces. This is why you can heat, for example, a 36 unit 40,000 square foot 4 floor apartment building evenly (with proper venting!) with NO zone valves, NO electronic controls, NO circulating pumps, NO room thermostats, NO mixing valves, NO blowers, NO radiator bleeding, NO expansion tanks, NO freeze protection, NO static head pressure. Just automatic vents. Which are cheap in comparison.
    I will take this opportunity as a steam heat advocate to take some lumps from the hi-tech hydronics guys who are justifiably proud of the truly remarkable strides they've made in fuel conservation technique. Steam has been soooo stuck in the post WWII intermittent firing, cast iron boiler, oversized, fuel-is-cheap world. Ironically, steam heat fuel conservation was developing into a high art in the hand fired and stoker fired era. Even some of the gas boiler manufacturers were trying for economy with clever design and firing rate/damper modulation. But the clever ideas never survived the post war fast and cheap mindset. Hydronics at the time didn't fare much better. And everything had to compete with forced air in first cost. But along come the new modulating condensing hydronic boilers, and steam boilers (since they're for "replacement only") have been caught with their pants down for a few years. Finally we're seeing good stuff coming along for our steam systems.
    The only area of contention is that the steam temp is high enough that operation in condensing mode and related fuel savings are not possible. I disagree, since discrete devices have long existed to extract waste heat from industrial steam boilers. Preheating return condensate is a great place to put it. Condensing economizers exist for this purpose. Combustion air preheating exists and is useful as well. Small packaged versions of these things would put steam ahead of the pack, but we won't likely see them soon, if ever. They would be separate packages of sufficiently high cost that the payback period would be very high, and ROI might be non-existent in the life of the product. A familiar arguement in hydronics world.
    -Terry
    Terry T
    90%+ boiler efficiency is possible on steam
    Gasmaster in Canada and Hoval in the U.K. do it on larger boilers. There really is no reason we can't have it here in residential units except that American boiler manufacturers won't step up to the plate, similar to the situation where some boiler makers won't sell their wet-base oil boilers with power gas burners. Whoever gets off their butt first will sell a LOT of steamers.
  • ttekushan_3
    steamhead,
    it seems to me that the only reason any of these thing have happened in Canadia (my Canadian friends hate it when I do that) and the EC specifically is that its
    --Government Mandated-- (imagining the voice of God works well here).
    When some of those rules start heading our way in the next couple of years, we may see positive changes in home steam boiler design.
    Just another reason that I've told clients to hold off on a new gas boiler for now. Obviously I only advise this if their old beast is operating moderately efficiently and absolutely safely. These boilers I'll go ahead and do complete waterside and fireside cleanings, and combustion adjustments.
    My only fear is that some government people incapable of systems approaches and no-common-sense, think-inside-the-box, paint-by-numbers nitwit bureaucrats will push for the conversion of all steam heating systems to forced HW with the HVAC industry in gleeful support. And I truly believe its a real threat, given the prevailing views of the HVAC industry and the general nature of bureaucrats.
    -Terry
    Terry T
    Might not be that bad
    if we tell the little old lady with the steam system that if her boiler dies the government wants her to tear the whole system out and replace it, she's going to help vote the bums out! Remember, seniors are probably the biggest group of voters right now..... used to be baby boomers but they all got old.....
  • Cosmo_3
    Cosmo_3 Member Posts: 845
    awesome thread
    The more I learn from these guys the more I get excited about touching more steam work. It reminds me of when I started getting into hydronic radiant many years back.
    Looks like steam may have a bright future!
    Cosmo
  • Christian Egli_2
    Christian Egli_2 Member Posts: 812
    No faulty steam, faulty math
    Chopping percentages is like chopping earth warms
    Remember the high school algebra problems where we had to find the distance between two points knowing trains A and B were speeding towards each other and yadiyadiyada? The creative student writes down various plausible equations, confidently solves them for x until the beautiful answer appears: 0 = 0. Dang, now the bell rings and the test is over.
    Dear BC, I think you've been very creative, you first admitted half the radiators are turned off. No problem. That leaves us with 50% output. No problem so far.
    Then, in a more circuitous way, you went down a different route looking at BTU/h outputs factored with the contributions the boiler makes to the birds (78% net for us in this case). What your math is attempting to show is that if we assume 100% radiators connected and a 78% efficiency, then for 50% connection we should get 38% (about half of 78) - this bird does not fly.
    I have not wrapped my mind around showing what you're after BC but a more correct way to do it would be with the use of a condensate meter. Does your system balloon up into higher pressures? What happens if you open more radiators? Does the burner burn continuously all the while there is a call for heat?
    We've got the 7.5 hours weighted average down to 113F for what's inside the pipes. For the iron pipes themselves and the radiators - which give off heat all the while they're cooling off - we could also compute the weighted average. You've got nicely plotted curves, simple integration of those bumpy lines over time would yield that number for the iron mass (providing you glue your thermometer to the iron mass, which is not the subject of your current plot).
    From the current graph, you could integrate your weighted average indoor temperature, which, in all practicality would be your desired thermostat set point. Say 68F - a set back scheme would lower it. Meanwhile that same number for the iron mass would have to fall somewhere in between 113F and 68F.
    That's a management company problem
    they were probably the low bidder when the previous contract ran out. We all know about low bidders. The building owners will get what they deserve.
    Come to think of it, I've never had to replace a cracked steam boiler that had a probe-type LWCO on it. All the ones I've done had floats. I'm sure probes go bad too, but personally I haven't had to replace a boiler because of a bad probe.
  • BC
    BC Member Posts: 28
    A slight misunderstanding...
    Sorry I wasn't more clear. I wasn't trying to say that the fact that 50% of the original radiation was off made the system eficiency 50%. I'm sure the fact that the boiler is now oversized for the radiation load does not help the efficiency, but I doubt there's a linear relationship like that.
    I got the 50% number by taking the net input to the boiler (1.4gh*138500btu/gal*78% steady state eff*7.5 hours/24 hours) which is about 47mbtu/hr averaged over the day. I then took your average temp of 113F and multiplied it by the square footage of active radiation and then by 1.7btu/hr/ft2 which I think is the correct coefficient. This gives me about 23mbtu average that the radiators are delivering to the space. This is less than 1/2 the input to the boiler, hence the 50% number.
    There are 2 big assumptions here. The first is that the average radiator temp is indeed 113F over the course of the day. As I said I think this is low and I'll try to measure this soon to confirm. The other assumption is that the radiator output scales linearly with temperature. THis may not be a bad assumption as most output charts I've seen for panel radiators and the like are pretty linear.
    You are correct of course that the way to get a definitive answer is to integrate the radiator temp and room temp over a period of time - this is what I'm going to do as soon as I get a sensor on the surface of the radiator.
  • BC
    BC Member Posts: 28
    Very true
    This is in no way an optimized system. It is vented and balanced pretty well, but the boiler is sized for about 750ft2 of radiation and there is about 300ft2 currently turned on. The boiler is drastically downfired, but it is still almost double the firing rate it really needs. It needs to be replaced and it will be intersting to see how much more efficient a properly sized unit will be.
    Could you
    please take some pics of your measuring setup? We have a couple of systems I'd like to try it on.
  • ttekushan_3
    In reviewing this
    "drastically downfired" keeps coming back to haunt me. You can only downfire so far before the firebox becomes a cavern in which the flame gets lost. I hope that the downfiring was done in the context of a running combustion analysis so that excess air is not extreme. If draft is not properly controlled as part of the downfiring, you've lost a tremendous amount thermal transfer efficiency regardless of the combustion efficiency numbers.
    Is this why so many radiators are closed-- fuel consumption is totally out of control?
    I'd bet that a boiler sized for the total load of all the radiators open that could modulate downward (or a dual boiler setup described elsewhere) after steam is established would use less fuel with all the radiators open than your current boiler with half of them shut off.
    Terry T
  • The problems with steam, as I see it...
    as our gracious host has so aptly put it, is that it is a "Lost Art".
    The few people who are still on this side of the lawn, that truly understand all of the physics associated with these labor intensive systems are retiring and or going to the other side of the lawn faster than replacement techs can be trained and brought on line, taking critical information with them when they go.
    There is definatley a romanticism about steam. Without it we wouldn't have had an industrial revolution, and without that, we probably wouldn't be here today because we would have been wiped out by typhoid, cholera, dysintery or any of a thousand other rampant diseases prior to the industrial revolution.
    The most knowledgable people on steam hang out at this web site, and I can count them on one hand. And none of them is getting any younger. The new "kids" coming into this system of technicians has little understanding of how hydronics work, much less something as delicate and complicated as steam, and most of them are working on a commission basis, so from their stand point it makes more $en$e to rip out the old, and throw in a new mod con (assuming salvagable 2 pipe system here) and go on down the road to the next one.
    Sad to say, but true...Tis a Lost Art and dieing off fast.
    ME
  • ttekushan_3
    \"And none of them is getting any younger\"
    Hey! I've been 39 for the last six years. What about that?
    Seriously, the expertise on steam systems is minimal.
    But you mention hydronics in general. I think this is true also. I do steam, but I get referred to simple, classic pumped HW systems with a few zones more and more frequently and there they are all screwed up and not heating properly--just like the steam systems. The problems are different but no less maddening in their origins in "service work gone wrong." And the solutions are simple if you've bothered to read a book (or this site) at all. The trail of destruction is remarkable.
    I hate to think the only heating system that will succeed is one that never requires service of any kind until it fails completely in 7 or 10 years and gets wholesale replacement. Just like the consumer electronics industry. Not much comfort there.
    True story: A camera shop I once frequented had a cartoon taped inside the glass counter. It was "Shoe" by Jeff McNelly.
    A guy goes into a camera shop and says "I need a totally idiot proof camera."
    The shop owner says, "Here. This one does everything automatically. You don't have to think. Completely idiot proof."
    The customer leaves with his new idiot proof camera.
    The shop owner says, "I don't know how long I can stay in business selling cameras to idiots."
    My camera shop's out of business.
    -Terry
    Terry T
    But if the conversion goes haywire
    as so many steam-to-water conversions do, does the know-nothing kid still get his commission?
    I hope not. That would be sheer insanity. If I were his boss he would get NOTHING from a botch job like that. I'd probably fire him for costing the company so much call-back money.
    Which begs the question: if these kids know nothing about steam, what are they going to know about mod-con hydronics? Probably the same- nothing at all.
    And very few of these kids want to learn, or improve themselves in any way. We have no use for them- that's one reason it's just Gordon and me. Maybe we'll get lucky, but from what I've seen around here I doubt it.
  • I feel your pain Frank...
    And I agree with you about paying these kids for botched jobs, but the government disagrees with BOTH of us.
    At present, the mentality of a lot (not all) service/repair companies (especially flat rate companies) is to hire a saleperson and teach them how to plumb/replace heating systems.
    I get SO tired of emergency orphan calls, I can't tell you... But they do bring in just rewards for the company, so we continue our "adoptions"...
    We find ourselves in a pickle at present. We need additional help. It has been our experience, that if you hire an experienced plumber, and try and teach them your way of doing it, they bring along "baggage" that causes YOUR product to suffer. SO, do you take the time to hire a person who is mechanically adept and has a good work ethic (knows how to use wrenches and tape measurers and gives 8 hours of work for 8 hours of pay and will work overtime if required) and raise them they way YOU want them to be raised, or continue hiring experienced carpet baggers who know how to solder, and bluff their way through a system...
    I know what I'd LIKE to do, but it doesn't fit within the current scope of employment ;-)
    ME
    The government can't disagree
    if you have this spelled out in a contract or similar document with the employee. If they agree by signing, I don't think the government can intervene at all. This goes all the way to the Constitution which prohibits anyone, government included, from interfering with the obligations of a contract.
    Of course we'd get our lawyer to write such a contract.....
  • BC_3
    BC_3 Member Posts: 12
    I'm using Dallas 1-wire sensors
    I'll try to take some pics tomorrow, but it is nothing fancy, just Dallas 1820 and 1822 sensors (http://datasheets.maxim-ic.com/en/ds/DS18B20.pdf) hooked together with an assortment of cat5, telephone wire, etc, whatever is handy at the time. They seem pretty tolerant of sloppy wiring! They are robust, cheap, and you can string dozens of them along the same 2 or 3 wire cable.
    I'm planning on getting a WEL from Phil Malone (http://www.ourcoolhouse.com/WEL/) when finances allow. Now the 1-wire network is hooked into my weather station software running on an old PC, which allows logging but nothing fancy.
    The system ain't pretty, but it gives me tons of sensors with +/-2deg accuracy and I have less than $50 in the whole thing.
  • BC_3
    Cavern is the right word
    for the firebox in this boiler! I'm not sure when it was downfired, it has been this way since I moved in 7 years ago. I think the original rating was 2.75gph. Somewhere along the line a Quickie 200 chamber was fitted so that is in the right size range for the current firing rate of 1.4gph rate at least. Your comment about excessive air is interesting - it does seem to require a lot of air to get a clean burn - I've never seen the CO2 much higher than 8%. I haven't pushed the oil guy to really optimize nozzles etc, because every year I think that it will be the last year for the old beast and I'll get it replaced. I've been saying that for 6 years now!
    I'm curious about your comment on efficiency - shouldn't the combustion efficiency account for any excess air/draft? I always thought the traditional way of measuring combustion efficiency was basically calculating the amount of air (from Co2 or O2) and temperature going up the stack, and assuming all the rest of the heat went into the boiler. I don't disagree that it is not a good situation for efficiency, but I think if it was fired much higher it would short-cycle.
    The radiators are shut off since I am not using the upstairs of the house while I'm renovating. Also as I insulate and tighten the house even the downstairs radiators are becoming way oversized for the load.
    Amen to the system wanting a variable firing rate burner. I'd love to find something priced and sized for a residential application. I think once the boiler is "right-sized" it won't be as much of an issue, although as you and others have said even optimized steam systems should benefit from variable firing.
    Looks like you're in the market
    for a Burnham Mega-Steam boiler!
  • Sorry, Frank.
    Not trying to raise your blood pressure. But, that was far from an isolated incident. D. C. Schools can't keep sections in steam boilers that were installed 2 & 3 years ago. Contracting restrictions dictate who puts them in. DCMR mandates who maintains them. Worst of both worlds. Indifferent installations & worse maintenance. Guess who is being blamed? You got it.
    How about that Property Manager? The heating firm he hired is one of the biggies. You know. Beach condo. Fishing trips. Vegas, if you prefer. And a sales type hovering like a vulture waiting for the boiler to crack. Our fishing trip is for employees & families only.
    We haven't replaced a boiler because of probe failure either. Try to catch failures w/ proactive maintenance. Have replaced several probe types that failed w/ the circuit made. Don't rely on test buttons anymore. Not since the local Hartford Inspector whispered in my ear that he found 3 of 4 unsafe on high pressure boilers @ the same complex, even though the test button lit up. It's still satisfying to open the blow down valve & hear the burner shut down. That's what I mean by "hands on."
    Have you seen a computer operated mechanical room yet? I have. A few were well kept. The rest never saw a human unless the 'puter said something was wrong. Try a steam boiler in that environment.
    The world is a-changing & steam systems, as we know them, are not included. Dang shame.