you've got a riser within 6-8" of the end of the main. That means that riser won't heat properly (if at all) using the ideal option #3.
You'd have to extend the end of the main at least about 2' past that riser (with a t for the vent manifold of course) and repipe the drip to match.
You'd have to extend the end of the main at least about 2' past that riser (with a t for the vent manifold of course) and repipe the drip to match.
0
Comments
-
Venting Mains - Which is my best option? Thanks.
I've purchased 3 Gorton #1's to vent the longest main run but I'm at an impasse as to which is my best option. I've drawn a really rough (I'm no artist) sketch of three options that I've come up with by piecing together advice from Steamhead, others and Dan's book. The drawing is of the end of the main where it bends down for the return which you can see clearly in the photo attached below.
Which of the options in the drwaing below is my best bet and if not one of these three, what other options do I have? Thanks for any help with this!
P.S. Here is the link to my previous post...
http://forums.invision.net/Index.cfm?CFApp=2&Message_ID=199540#Message1989730 -
Steve, there is another current post where a guy shows his Hoffman 75's venting through a ceiling cutout. Is that a plaster ceiling that can be cut to give you more room? Or is it concrete (like mine). Can't tell.
Here is the thread:
http://forums.invision.net/Thread.cfm?CFApp=2&Thread_ID=30453&mc=120 -
Unfortunately...
It's solid concrete. I wish I had room for a Gorton #2 or a Hoffman 75 and then I'd be done with it. Then again, Dan does say in his book that it isn't good to have a main vent at the end of the main because it makes the vent vulnerable to being damaged.
Perhaps the first option is best then??? I'm not sure. Thanks!0 -
I like #1 the best
since it gets all three vents away from the tee in the main. With #2, the center vent is right over the tee in the main so it could get hammered. And you don't have room for #3 because of that riser so close to the end.
Go with #1.0 -
Sizing of pipe for the T
Thanks everyone for the quick replies.
So it looks like option #1 is my best bet but I forgot to ask in my original post what size of piping I should use for the T? I'm guessing 1" to 1.5" in diameter???
Thanks again.0 -
pipe size
3/4" should be good enough. as per gill & pajek's chart
mark sch0 -
One thing to keep in mind
While #1 is a good option, I'd imagine that the main there is probably tilted downward moving to the left of the picture. As such, beware if everything else is at right angles and you tack on the extra vents exactly as #1, since that would presumably mean that condensate will collect at the far left end of the pipe. Perhaps you'll want to give the whole thing a 180 degree twist about a vertical axis.
-Michael
0 -
Mike, you're absolutely right
Make sure the horizontal pipe has a slight pitch back to the main.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements