Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Outsoor reset control for Peerless Pinacle
M. McDonnell
Member Posts: 3
Dear Big D. To allow for modulation on the boiler with your outdoor reset you must convert to the 125 board. Once converted the boiler can use the Pavilion 410 control to give you outdoor reset and all the benefits of the modulating Pinnacle boiler. There are also Tekmar controls that can be used along with an interface module available from your Peerless distributor.
WHA boards can work with outdoor reset controls but the modulation feature of the boiler will not be fully functional.
WHA boards can work with outdoor reset controls but the modulation feature of the boiler will not be fully functional.
0
Comments
-
Outdoor Reset Control for Peerless Pinnacle
I have a Peerless Pinacle with the WHA control Board. I want to install an outdoor reset control. Does Tekmar or some other company have an outdoor reset control that will work with my WHA control board of do I have to get a new P-125 control Board.0 -
tekmar
with an Interface board from Peerless, you could use a tekmar 270 Boiler Control to modulate the Pinnacle.
I hope this helps. If you have further questions, please feel free to call tekmar at 250-545-7749.
regards,
Mike0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements