Baseboard/cast iron radiator on same zone
Tony Campanella
Member Posts: 1
Hi,
We are doing some renovations. To make a long story short - A new zone I added has all copper basebaord, hot water heat. A small radiator I moved from the main part of the house is very close to that area and a lot easier to access fromt he new room.
Can I put these on the same zone ?
Thanks
Tony Campanella
Home owner
We are doing some renovations. To make a long story short - A new zone I added has all copper basebaord, hot water heat. A small radiator I moved from the main part of the house is very close to that area and a lot easier to access fromt he new room.
Can I put these on the same zone ?
Thanks
Tony Campanella
Home owner
0
Comments
-
Not wise!
Cast iron radiators and copper fin baseboard have GREATLY different requirements and emission characteristics. Balancing the two in a single zone will be darned near impossible.
How are you controlling the new zone? Copper fin baseboard is almost certain to need higher temps that your iron radiators. You should never assume that iron rads are operating at 180° even in the coldest weather...0
This discussion has been closed.
Categories
- All Categories
- 87.2K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 427 Carbon Monoxide Awareness
- 117 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 111 Geothermal
- 163 Indoor-Air Quality
- 3.7K Oil Heating
- 72 Pipe Deterioration
- 1K Plumbing
- 6.4K Radiant Heating
- 393 Solar
- 15.5K Strictly Steam
- 3.4K Thermostats and Controls
- 55 Water Quality
- 51 Industry Classes
- 49 Job Opportunities
- 18 Recall Announcements