Big Ed
Member Posts: 1,117
Wire both zone valves to the thermostat with the largest load and reset the antisipater to the new current draw.....
0
Comments
-
proper relay setup for 2 zones on 1 stat
For hydraulic reasons, I need to make 2 smaller zones in a space that really only needs one stat. Assuming Taco zone valves and a standard 24V setup, what's the right way to do this?
thanks.0 -
Wire zone valve 1 to thermostat. Wire end switch of zone valve 1 to open zone valve 2. Wire end switch of zone valve 2 to start circulator.0 -
If they're Taco 500 series, can a Honeywell CTIII handle what I think is 1.8A? (0.9A each)? I thought most stats can only handle up to about 1A. But I'm somewhat ignorant about this. thanks.0 -
sounds logical. Is this a common situation? thanks.0 -
I think I would splice a single thermostat wire into both zone valves so when the zone's thermostat called for heat both zone valves will open0
This discussion has been closed.
Categories
- All Categories
- 87.7K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 430 Carbon Monoxide Awareness
- 129 Chimneys & Flues
- 2.2K Domestic Hot Water
- 6K Gas Heating
- 122 Geothermal
- 170 Indoor-Air Quality
- 3.8K Oil Heating
- 79 Pipe Deterioration
- 1.1K Plumbing
- 6.6K Radiant Heating
- 396 Solar
- 16K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 17 Recall Announcements