2-pipe gravity return vapor system without main traps?

Garret
Member Posts: 111
(I'm reposting in its own thread... I thought the old thread might be getting a bit unwieldy.
http://forums.invision.net/Thread.cfm?CFApp=2&Thread_ID=34889
)
A bit of a follow-up to the above discussion... I ordered all of Dan's books, and have been reading through em, trying to understand my system as much as possible.
Here's one thing I'm puzzling about. I have a two-pipe, gravity return, vapor system. I have traps on every radiator, but as far as I can tell, I have no traps on the ends of the steam mains.
I have two mains, that wrap around the basement, and meet on the other side in a tricky bit of piping. Basically, each takes a turn downward, and runs to the floor, where they meet and a pipe runs over to the wet return. There are vents at the top (there's a big hoffman on one, and I noticed there's a little metal vent tapped into the other one), but nothing on the bottom except a few T and elbow fittings.
If you'd like to see it, start at this photo, and take a look at the next four or five.
http://www.worksongs.net/photos/2006-02-Boiler-Replacement/slides/IMG_7899.html
In this arrangement, do I not need "end of main" traps at all? I've looked over the system several times, and I just don't see em.
Best, -Garret
P.S. Things are going well with my little project... I've had several contractors look over the system, and I think I've found at least one who knows what he's looking at. I'll keep you all posted on the process as we get further along.
http://forums.invision.net/Thread.cfm?CFApp=2&Thread_ID=34889
)
A bit of a follow-up to the above discussion... I ordered all of Dan's books, and have been reading through em, trying to understand my system as much as possible.
Here's one thing I'm puzzling about. I have a two-pipe, gravity return, vapor system. I have traps on every radiator, but as far as I can tell, I have no traps on the ends of the steam mains.
I have two mains, that wrap around the basement, and meet on the other side in a tricky bit of piping. Basically, each takes a turn downward, and runs to the floor, where they meet and a pipe runs over to the wet return. There are vents at the top (there's a big hoffman on one, and I noticed there's a little metal vent tapped into the other one), but nothing on the bottom except a few T and elbow fittings.
If you'd like to see it, start at this photo, and take a look at the next four or five.
http://www.worksongs.net/photos/2006-02-Boiler-Replacement/slides/IMG_7899.html
In this arrangement, do I not need "end of main" traps at all? I've looked over the system several times, and I just don't see em.
Best, -Garret
P.S. Things are going well with my little project... I've had several contractors look over the system, and I think I've found at least one who knows what he's looking at. I'll keep you all posted on the process as we get further along.
0
Comments
-
it appears your
mains drop to a wet return..no traps needed..better air venting on the one would be in order tho..
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0 -
Ah, okay... that's makes complete sense. Steam can't get by water. Thanks, Gerry!
0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements