Steam main air removal?

Jamie_6
Member Posts: 710
Just wanted to make sure these numbers are correct.
100' of 2 1/2" pipe = 3.32 cubic feet of air.
50' of 1 1/2" pipe = .71 cubic feet of air.
40' of 1 1/2" pipe = .54 cubic feet of air.
110' of 2 1/2" pipe = 3.32 cubic feet of air.
Also does any one have information on Gordon #2 so I can determine how many vents we need for each main?
Jamie
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=289&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
100' of 2 1/2" pipe = 3.32 cubic feet of air.
50' of 1 1/2" pipe = .71 cubic feet of air.
40' of 1 1/2" pipe = .54 cubic feet of air.
110' of 2 1/2" pipe = 3.32 cubic feet of air.
Also does any one have information on Gordon #2 so I can determine how many vents we need for each main?
Jamie
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=289&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
0
Comments
-
hey jamie
Got to books and more,third one down.gerry gill and steve pajek put a nice pice together,have a happy heating season everybody!
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
The only error I can see
is that 100 feet of 2-1/2" is 3 cubic feet even, not 3.32. Everything else looks great.
I'll second Paul, get Gerry and Steve's charts. The cost of $10.00 is very reasonable and it all goes to charity.
You can see the results of using these charts in my All Steamed Up/Calvert Court posting. They were much more accurate than anything I've seen including my old ones. We had to do a bit of fine-tuning, that's to be expected- but the amount of fine-tuning was lower than on any previous job.0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 105 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 69 Pipe Deterioration
- 949 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements