Anybody make 11/2\" TRV valves? PGP
tim smith_3
Member Posts: 4
> Anyone know where to find 11/2" TRV valve bodies <BR>
> in angle or reverse angle? <BR>
> <BR>
> Danfoss makes <BR>
> 11/4" TRV's, I've used Oventrop metric 11/2", but <BR>
> they're custom ordered from Germany with a <BR>
> 4-6week order lag. As gravity systems are <BR>
> converted, it's difficult(if not impossible) to <BR>
> revalve the radiators to a smaller size. I wish <BR>
> Danfoss would make the 11/2"...I'll add it to my <BR>
> hydronic wish list.<BR>
> <BR>
> _A <BR>
> HREF="http://www.heatinghelp.com/getListed.cfm?id= <BR>
> 104&Step=30"_To Learn More About This <BR>
> Professional, Click Here to Visit Their Ad in <BR>
> "Find A Professional"_/A_ <BR>
<BR>
> in angle or reverse angle? <BR>
> <BR>
> Danfoss makes <BR>
> 11/4" TRV's, I've used Oventrop metric 11/2", but <BR>
> they're custom ordered from Germany with a <BR>
> 4-6week order lag. As gravity systems are <BR>
> converted, it's difficult(if not impossible) to <BR>
> revalve the radiators to a smaller size. I wish <BR>
> Danfoss would make the 11/2"...I'll add it to my <BR>
> hydronic wish list.<BR>
> <BR>
> _A <BR>
> HREF="http://www.heatinghelp.com/getListed.cfm?id= <BR>
> 104&Step=30"_To Learn More About This <BR>
> Professional, Click Here to Visit Their Ad in <BR>
> "Find A Professional"_/A_ <BR>
<BR>
0
Comments
-
Availability...
Anyone know where to find 11/2" TRV valve bodies in angle or reverse angle?
Danfoss makes 11/4" TRV's, I've used Oventrop metric 11/2", but they're custom ordered from Germany with a 4-6week order lag. As gravity systems are converted, it's difficult(if not impossible) to revalve the radiators to a smaller size. I wish Danfoss would make the 11/2"...I'll add it to my hydronic wish list.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
I had
the same problem on a gravity conversion and couldn't find anything. I had to cut the old 1½" risers down about half way and thread them in place to screw on a 1½" x 1¼" bell reducer.
You've got to do it with 2 guys, one guy on the threader and one on a pipe wrench to back it up. And be careful not to get any threading oil on the wool carpet. |:0
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
thread in place
try it with a ridgid 700 .the wrench locks against the machine making it a job a girl could do by herself. a big girl. lol0 -
Paul, Try HW Braukman, I just did some, i think they were 1-1/2\"
0 -
too bad....
HB makes up to 11/4" only, Tim.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements