Could use a little strategy advice

Bob Sweet
Member Posts: 540
Relacing 80% boiler with new Ultra. 3 zones radiant 1 zone BB and indirect heater. Unfortunately the radiant zone minimum supply temp will be 125* due to construction factors I cant change (tube layout and manifold placement)however BB zone will work with supply temps of 160*. Looking for idea's on pumping strategy, mixing, tempering valves. Trying to offset the rad. supply temps with some creative pumping. Any ideas? Thanks
0
Comments
-
Advise
tekmar Controls: Boiler Reset Module 422 with Zone Manager 337 with 541/542 thermostats with 3-Way Brass Mixing Valve and Actuator.
Please call for piping strategies.
Regards,
Mike 250-545-77490 -
are you also considering an indirect tank?
Radiant supply temps of 125F, DHW, even BB at 160F all will benefit from a condensing boiler. The greater the condensing surface area the greater the savings. Throw in a modulating Matrix burner and voila, money in the bank.
Remember, BB only will require 160F during the design time. All of the heating season approaching and departing from the design temperature will operate at lower temperatures.0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 105 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 69 Pipe Deterioration
- 949 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements