Belt Driven Blowers
Eugene Silberstein 3
Member Posts: 1,380
I was asked to repost this item about approximating the length of a belt that should be used on a belt driven blower assembly. In the figure, R1 and R2 represnet the radius of the drive pulley and the radius of the driven pulley. D represents the center-to-center distance between the two shafts.
Since the belt goes around approximately half of each pulley, the length needed to go around half of each pulley is equal to one-half of the circumference of each pulley, or 0.5(2)(3.14)R1, and 0.5(2)(3.14)R2. This simplifies to
3.14 (R1 + R2)
To this we add twice the center-to-center distance between the pulleys, or 2D.
So, the approximate length of the required belt is about:
2D + 3.14 (R1 + R2)
Consider this example:
Two pulleys with diameters of 4 and 6 inches, with shafts that are 12 inches apart.
The approximate belt length is:
2(12) + 3.14(2 + 3) = 24 + 15.70 = 39.7 inches.
Just to be on the safe side, have a 40" belt on hand, as well as one size up and one size down.
Enjoy.
Since the belt goes around approximately half of each pulley, the length needed to go around half of each pulley is equal to one-half of the circumference of each pulley, or 0.5(2)(3.14)R1, and 0.5(2)(3.14)R2. This simplifies to
3.14 (R1 + R2)
To this we add twice the center-to-center distance between the pulleys, or 2D.
So, the approximate length of the required belt is about:
2D + 3.14 (R1 + R2)
Consider this example:
Two pulleys with diameters of 4 and 6 inches, with shafts that are 12 inches apart.
The approximate belt length is:
2(12) + 3.14(2 + 3) = 24 + 15.70 = 39.7 inches.
Just to be on the safe side, have a 40" belt on hand, as well as one size up and one size down.
Enjoy.
0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements