Steam Question
Rookie_3
Member Posts: 244
Haven't ran into too many steam boilers until recently and they have been basic clean and tune up. Had one today that ran good but the water in the site glass was going up and down.
Any causes or cures would be appreciated. Nothing looked unusual except for that.
Thanks.........ROOKIE
Any causes or cures would be appreciated. Nothing looked unusual except for that.
Thanks.........ROOKIE
0
Comments
-
Surging water line, could be dirty boiler water or a skim of oil on top of the water. the water has to boil violently to break through the oil causing the site glass to surge. Violent boiling throws water up with the steam, and can cause wet steam . You loose some efficiency with wet steam. Read about skimming a boiler in the owners manual or ask your boss Im sure he knows. The oil comes from pipes being worked on or a new install usually. I have heard that faulty near boiler piping can also cause this but I dont know why.0 -
Sounds like your right on. The house has just been through a total rehab and the boiler was drained for the summer with the feed pipe cut out and a new pipe was brought in from another direction of the basement. I kept blowing it down and would get dirty water after it ran for a while.(black) The up and down movement is steady but not real harsh. Thanks, guess I better do some reading on skimming...............ROOKIE0 -
surging
If you are maintaining a boiler, I'd recommend several of the books Dan Holohan offers here at HeatingHelp.com. Reading the "Steam Problems" section would be a profitable start.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements