Which steamer?!
adambuild
Member Posts: 414
Calculated 218.5 square feet of radiation which imho would need a boiler with gross input of 78MBH. Client wants a Weil McLain. Question: 2 PEG models available PEG30 @ 75MBH input or PEG35 @ 100MBH input. Which one?
Thanks in advance, Adam
Thanks in advance, Adam
0
Comments
-
adambuild
Go with the peg35, if my memory serves me its around 250+ and I think the 30 is under 200. Its actually the same boiler with a larger (1 extra burner) gas train.
I rarely post pics but we recently started doing residential installs again so here goes.