co detectors for boilers
PS
Member Posts: 49
Just had my new VM direct vent (Vitodens)inspected this month - he never said a word about the hardwired CO detector! I have (2)CO detectors upstairs in living areas - I know he didn't see them.
0
Comments
-
ma. code and co detectors
i just installed a munchkin boiler and gas inspector wants me to hard wire a co detector with the boiler per new addendum in ma code.
The problem i am having is that i dont know what style to install? Any one in ma have info regarding what type of detector to install, in regards to what manufacturer to install and what the code book says.
I was not aware of this new rule and the inspector only told me i need one he couldnt give any insite on a particular brand.
Any info would be great0 -
boy that sucks just another thing for electricians to f up.
0 -
link to changes
http://www.mass.gov/dpl/boards/pl/cmr_prop/amend248cmr5_08.pdf
There ya go basicly any 110volt with battery backup, Waiting for the day a gas and electric inspector are in the same room fighting over whose code gets followed0 -
CO detectors
You may bwant to talk to Dennis Driscoll the Middleboro inspector. At last nights Inspectors meeting this was the hot topic and no one was sure whats going on.0 -
Excuse my bluntness,
but they should look at their mail and be in touch with their own Board.
This has been on the books since July 29th to the complete shock of many including me, but there were not a lot of inspectors at the last two meetings I went to in Boston, FACT!
This action even circumvented the AG and Sec. of State's Office, go figure that one out.0 -
Dennis is no
longer the Middleboro inspector, he is now a state investigator. However, he is still a great source of information.
The code changes are far from perfect, they are still a work in progress, at this time, they only apply to direct vent units.
There is still a lot of work to do in this area, but it is a start. The next step as I see it, is to get mandatory testing for any installed gas appliance, it has to be done for oil. I cant understand why we are not required to do it for gas. I think this would go much further than what they are doing now.
Chuck0 -
Chuck this came up
at the Gas Networks Meeting recently. A very popular TV personality/contractor basically let it be known that contractors should not be required to do any testing on gas equipment that they install. He stated that the gas company should be doing all testing. He made it pretty clear that contractors are not going to spend any money on combustion test equipment. If the state of Mass can make it code for doing testing and require everyone to be trained then Firedragon is going to have alot of work. This personality has a lot of peoples ears so I know he will be a strong influence against contractor testing.
It is a definite that the utilities are not going to do it as they are getting out of doing any kind of service.
I find it intersting that just afew years ago the contractors wanted to take the utilites to court to force them to stop doing service. Now they want it the other way.
I was turned down by the Mass Board for doing any training of contractors due to the fact that I do not have a gas fitters liscense and therefore as the board stated am not a qualified gas trainer.0 -
Anyone who proclaims
that testing is not required is sadly messed-up. I don't care who he is or more importantly who HE thinks he is, period.
I'm a registered expert witness in 20 states and have had cases involving the gases (Nat and LP), oil and waste oil. I can't even begin to tell you how critical combustion testing is.
How about a major soot and IAQ case that was lost over something as insignificant as blower motor rpm?
More importantly every code and I&O manual I've ever seen requires that it be done. How do you get around that?
To those that feel testing is not necessary, see you in court! I'll be the one with the box full of gauges and testers, FACT!0 -
Co Detectors
I was at the was at the Gasnetworks conferance too. It was not said that the co detector had to be hard wired. For direct vent boilers with vent terminations below four feet, there must be a co detector in the mechanical room plugged in to the same circuit as the boiler. and one co det. upstairs(bedrooms).
And if the vent terminates above four feet, one co det. upstairs.
There also must be a sign out side at the vent term. stating that there is a vent term there.
I'm 95% sure of this, but I'd like to hear from someone else that was there.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Ted I have a copy of the MA inspector's monthly newsletter which touches on this subject... When a direct or mechanical vent appliance is installed below four feet a.g. you must have a HARD WIRED co detector with a BATTERY BACK UP installed on the SAME 120volt circuit as the boiler (it was once thought that it had to interlock w/ the ignition circuit and shut off the power to the unit if co is detected, this apparently is not the case) you must have a battery powered co detector on each floor where there is a living space, a copy of the appliance's instructions specific to venting must be left onsite, a manf. approved vent termination must be used, and a sign must be installed four feet above the applicance vent with lettering saying 'gas vent below' when the vent is installed above four feet the only rules applied are the approved termination, install instructions, and the battery powered co detector rule where there is a living space.0 -
Thank you for explaining it.
EDIT: OK I read it a couple times and I do not see where it says the co det. HAS to be Hard wired.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
But what brand do you recommend?
It isn't code here yet, but I just started putting in gas equipment as gas is relatively new here. I have been putting in the "Nighthawk" type on every install just so that I can sleep easier at night. Are there better types on the market that you all are familiar with? Inquiring minds want to know,
Thanks
Rocky0 -
0
-
Real protection Rocky
comes from a low level detector.
Georger Kerr is the pioneer in this area and he has the "CO Experts" unit that I HIGHLY recommend.
Anything that is UL "approved" is useless, and I mean USELESS.
Do not kid yourselves folks, the UL listing is an absolute farce. You may think that one is better than nothing, but in reality one is NO different than nothing.
Attend one Jim Davis course and you will know what I mean. You will NEVER look at combustion and venting the same way again.
BTW, anyone been testing the new gas water heaters? What have you been finding for stack temps? I haven't tested one yet under 540 degrees diluted. That is above the limit for aluminum chimnies.
Mark H
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements