titlted water level EG
Options
Steamhead (in transit)
Member Posts: 6,688
it means the steam is having trouble leaving the boiler. Start by checking the following:
1- Is the low-water cutoff installed in the proper place on the boiler? If so, is it wired correctly?
2- Is the boiler piping done to manufacturer's specs? If this EG is a Weil-McLain and you have two 3" risers coming up from the boiler I would suspect that at least this part of the piping is OK.
3- Is the burner over-fired?
4- Is the boiler way oversized with regard to the system?
5- Is something in the system such as inadequate venting holding back the steam flow from the boiler?
6- Is the pressuretrol set too high, or is the pigtail plugged?
Let us know how you make out.
1- Is the low-water cutoff installed in the proper place on the boiler? If so, is it wired correctly?
2- Is the boiler piping done to manufacturer's specs? If this EG is a Weil-McLain and you have two 3" risers coming up from the boiler I would suspect that at least this part of the piping is OK.
3- Is the burner over-fired?
4- Is the boiler way oversized with regard to the system?
5- Is something in the system such as inadequate venting holding back the steam flow from the boiler?
6- Is the pressuretrol set too high, or is the pigtail plugged?
Let us know how you make out.
0
Comments
-
I have a boiler that will not call for feed, even when the water drops out of the glass. But if I shut off the gas flame, within a minute it will call for fill. It seems the opposite of the situation on page 50 of Dan's "Lost" book, because the "shallow" end is under the (2) 3 inch risers.
I thought about adding a probe, but there aren't any good choices left.
I skimmed it, and boiled the water on the stove just fine. Heats nice and quiet too.
Any help appreciated.0
This discussion has been closed.
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements