Rheem Boiler

WD
WD Member Posts: 5
Thanks I'll Give That A Try. But Still Cant Beleive Its Been Like That For 30 Years.

Comments

  • WD
    WD Member Posts: 5
    Rheen Boiler

    Went To Change Out Leakey Zone Valve On 30plus Yr Old boiler.Has Power Pile On Gas Valve.Ran Boiler After Changing Valve Pump Would Run All The Time With Zone Valves Closed 3 Zones.Their IS No Bypass Could This Be Possible.It Ran Like This For 30 Yrs.If This Is Wrong How Can IT Be Fixed.
  • Steamhead
    Steamhead Member Posts: 17,627
    Maybe the relay

    that operates the pump when one of the ZVs opens is stuck, or has been bypassed.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Ruthe  Jubinville
    Ruthe Jubinville Member Posts: 67
    Rheem boiler

    I know of one 007 that has been running all the time since 1990.
  • WD
    WD Member Posts: 5


    The Pump Is Wired To Run When The Power Switch Is Turned On.Will The Pump Be damaged If IT Is Left This Way.
  • Steamhead
    Steamhead Member Posts: 17,627
    I'm surprised it wasn't damaged already

    also now we know why the ZV leaked. I'd use an R845 relay to fix this- have the ZVs close TT on the R845, use the dry contacts on the R845 to operate the gas valve thru the high limit, and use the 120V contacts on the R845 to switch power to the circ.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting