Help Wanted
Steamhead (in transit)
Member Posts: 6,688
is likely not needed at all. That's a Vapor system which was designed to run on a half-pound of steam or thereabouts. With the proper pressure cutout, called a Vaporstat, the boiler pressure will be low enough that the water can return by gravity.
The Return Trap was essentially a pressure-powered pump, which served to return water if the boiler pressure got too high. This was how they solved the pressure problem before Vaporstats were invented. For a discussion of how it worked, see chapter 15 of Dan's book "The Lost Art of Steam Heating", available on the Books and More page of this site.
Have you found any names on the Return Trap or Vent Trap that would help us identify the system?
The Return Trap was essentially a pressure-powered pump, which served to return water if the boiler pressure got too high. This was how they solved the pressure problem before Vaporstats were invented. For a discussion of how it worked, see chapter 15 of Dan's book "The Lost Art of Steam Heating", available on the Books and More page of this site.
Have you found any names on the Return Trap or Vent Trap that would help us identify the system?
0
Comments
-
Help Wanted
We are looking for an experienced service/install tech. The / means good at both. Must know oil, gas, A/C. Great pay etc. All the benefits and truck. We are in NJ and do work in Monmouth and Ocean Counties. Please call our office 732-892-4957.
Thanks
Paul0 -
Steam return trap system
I am replacing piping on a return trap steam system that has previously been altered since being a coal fired system. 0002 picture shows a condensate reciever that was added at some time. I`m wondering if it is in the proper place in the system or if it was done incorrectly. The boiler is a Weil McLean gas similar to an LBG. I do not understand the return trap system and know it has not been maintained in years. I can replace the piping but would like to make the system better if possible. The condensate reciever also floods out the vent regularily.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements