? were KING valves full port

jesse the great
Member Posts: 72
I'm re-piping my steam boiler over the summer, and I'm going to install a 2-1/2 gate-valve for bottom blow down purposes and the gate-valve is not full port so I was wondering if the old KING valves were full port. I personally have not seen a king valve so I'm asking. also if the gate-valves ID is like 2" is that going to create an orfice and suck water or wet steam into the main and defeat the purpous of repiping. any insight would be great thanks
0
Comments
-
Yes they were
bush a 3-inch valve down if you have to.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Why not use a ball valve?
Either a full port 2 1/2 or a bushed 3".0