replace big steam boiler

bill nichols
bill nichols Member Posts: 4
I have a customer with a 15 unit apt building that needs a new 1 million BTU steam boiler. Well, at least there might be a million btu's of connected load, but the heat load in the building is only 750 mbh (domestic hot water from other boiler)
can i downsize the boiler?
Does anybody have experience with Tekmar's steam boiler control? It adjusts ON time with outdoor temp, measures condensate rtn temp, and 1 or 2 indoor temps.

Thanks

Comments

  • Steamhead
    Steamhead Member Posts: 17,384
    If you're not sure

    what the connected load is, the only way to find out is to measure the radiation. Size the boiler from that.

    What type of steam system is it? One-pipe? Vapor?

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Frank is right.

    > what the connected load is, the only way to find

    > out is to measure the radiation. Size the boiler

    > from that.

    >

    > What type of steam system is it?

    > One-pipe? Vapor?

    >

    > _A

    > HREF="http://www.heatinghelp.com/getListed.cfm?id=

    > 157&Step=30"_To Learn More About This

    > Professional, Click Here to Visit Their Ad in

    > "Find A Professional"_/A_



    Measure the radiation load before sizing boiler. The Tekmar 269 is an excellent control. You can add nite set back w/ a D076 Sensor & a clock. Or turn off heat to an adjustable O/D temp. w/ just a clock.