Steam tappings?
sandy
Member Posts: 4
I'm going to replace a Weil-McLain steam boiler, with either the same SGO-3, or a peerless. The existing feed is only two inches and the weil's tappings are 2 1/2. I heard you can't bush down steam lines. Is this true? Or can I use a 2 by 2 1/2 bullhead?
0
Comments
-
First build a header, equalizer and Hartford Loop
according to the piping diagram that comes with the boiler. Then take your steam mains off the header.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
steam tapping
First and foremost, use a Weil !!!!
Secondly, I agree with steamhead..never reduce the tapping size. Build a 2 1/2" header and equalizer per instructions and then go to your 2" piping, between the last riser and the equalizer. Weil provides very easy to follow piping diagrams with all their boilers.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Thanks. Steamhead and AL
Thank you for your advise and personal poinion on the boiler I know to go with trade reccomended products and mfg's.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements