Help wiring a VisionPro Tstat

Jamie, on your isolation relay, the purple dashed line needs to go to a common in the zone relay panel.

Then the blue dashed line needs to be moved from the C terminal to the R terminal.

The top two terminals on the relay being the coil, need a hot and a common, right now your are provding the coil with two 24 volt hots.

The two bottom terminals being contacts, when the contacts close, you are shoring W to C (hot to common). Moving the Blue from C to R will cause R and W to make when the relay is energized and the Hydro air will come on.