Help wiring a VisionPro Tstat
Glenn Harrison_2
Member Posts: 845
Jamie, on your isolation relay, the purple dashed line needs to go to a common in the zone relay panel.
Then the blue dashed line needs to be moved from the C terminal to the R terminal.
The top two terminals on the relay being the coil, need a hot and a common, right now your are provding the coil with two 24 volt hots.
The two bottom terminals being contacts, when the contacts close, you are shoring W to C (hot to common). Moving the Blue from C to R will cause R and W to make when the relay is energized and the Hydro air will come on.
Then the blue dashed line needs to be moved from the C terminal to the R terminal.
The top two terminals on the relay being the coil, need a hot and a common, right now your are provding the coil with two 24 volt hots.
The two bottom terminals being contacts, when the contacts close, you are shoring W to C (hot to common). Moving the Blue from C to R will cause R and W to make when the relay is energized and the Hydro air will come on.
0
Comments
-
Hey guys! Would someone be able to help me wire this bad boy?
1st stage heat is slab radinat
2nd stage heat hydro-air
Does this look right?
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Glenn,
Is this better? The change would be the dotted thick black line.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Same picture Jamie???
I don't see a change.0 -
-
Almost.
Right now you are using the common from the hydroair control, and W2 (hot) from the zone panel. You need to grab a common from the zone relay panel so you keep the two transformer sepparated.
Here's a modification. Sorry for the shaky lines. My mouse sticks.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements