Mod/Con pump location
Plumbob
Member Posts: 183
Pressure sensor. Pumping away from it could potentially trip it. Otherwise it makes no difference, as you said. Just be sure to use P/S pumping.
0
Comments
-
why pump in?
I'm seeing most of the mod/ con boiler piping schematics calling for the pump to be mounted on the return, pumping into the boiler. I was told this was to insure adequate flow, low mass, yada, yada. I don't get it. Isn't my rate of flow going to be the same through out my system? Can it change depending on which side of the boiler it's mounted on? I know I'll have pressure drop as my water circulates about, but can my flow rate change also? I don't see how. Maybe I'm missing something obvious...
Thanks for the help!
Still Learnin'0 -
Most mod cons
are high head designs so in order to keep the water from flashing into steam in the boiler you have to pump into the boiler. I generally think this is a waste of energy, since you have to pay to operate a much larger energy hog pump. Some mod coms are low pressure drop, like the Triangle Tube Prestige and Dunkirks, so they can be pumped away with a much smaller, less wasteful pump.
boilerpro0 -
The boiler likes to see
that pressure boost that the discharge side of the circ provides. It keeps the pressure switches "made" also.
Seems more and more of the Mod-cons are getting ported out HXers, and run fine with typical off the shelf 80 watt circs. The Knight, Prestiage, Bobcat to name a few.
Actually copper tube boilers have been showing pumps on the return for 20 years or more, that I know of. It's not a new or unusual concept.
hot rod
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements